Comms Rack Earthing and Bonding Question

Hi all


First post here, so apologies if I make any faux pas


I have a query on comms rack bonding (design stage).


- Two fibre services incoming to a big warehouse plus copper lines entering to a 42U cabinet in a small comms room on first floor of an attached little office area.

- MET is in the warehouse itself, in a corner (630A TPN supply).

- Fibre links from there to 5No. satellite racks (12U) on warehouse walls, 

- Satellite racks feed CCTV and WIFI in warehouse

- Light comms equipment install in the racks only.

- Furthest rack 240m away from MET (260m from comms room).


My question is about earthing and bonding to BSEN 50310.


Am I right in thinking that each satellite cab is to have a 4mm g/y to a brass earth block adjacent (secondary bonding busbar) and then connection onto a 16mm conductor back to a primary bonding busbar which in turn connects to the MET? Am finding the standard a little confusing. 42U to have a 16mm connection?


I see a table about sizing based on distance, but is that applicable?


Sorry if I am being dense, but finding it hard to understand. Help would be appreciated or direction to a simplified resource.


Regards


Muhammad







Parents
  • Thank you both very much for your replies, much appreciated.


    Sorry again for late response, but I tend to flit about here and there.


    Mapj1 - in answer to your question just standard and PoE switches and small rack mount UPS units (3kVA in the main rack, 1.5 in others), and that is it. Each cab location has a local DB next door - not dedicated to the cabs (other than main one), but just convenient to locate there.


    Tattyinengland - good point, it is also mentioned in the BSEN 50310 so can go that route. 




Reply
  • Thank you both very much for your replies, much appreciated.


    Sorry again for late response, but I tend to flit about here and there.


    Mapj1 - in answer to your question just standard and PoE switches and small rack mount UPS units (3kVA in the main rack, 1.5 in others), and that is it. Each cab location has a local DB next door - not dedicated to the cabs (other than main one), but just convenient to locate there.


    Tattyinengland - good point, it is also mentioned in the BSEN 50310 so can go that route. 