mapj1:
Inside equipment, because it can be type tested for approval (think of a megger-like test) you can show that an alternative arrangement is possible.
For example on a PCB with primary and secondary votages on the same side, I'd expect clearances to be to IEC-60950-1
it very quickly gets confusing. c
Agreed - BS 7671 does NOT apply to pre-manufactured assemblies, which should comply with appropriate standards (Regulation 113.1).
BS EN 62368-1 (IEC 62368-1) supersedes BS EN 60950-1 (IEC 60950-1) and BS EN 60065, both of which are due to be withdrawn this year.
Of course you can fit transformer in a CU. But unless the bellwires at 12 V or whatever coming out are over-sleeved to a standard that can hold off mains, you should really bring the ELV out in mains flex.
mapj1:
Inside equipment, because it can be type tested for approval (think of a megger-like test) you can show that an alternative arrangement is possible.
For example on a PCB with primary and secondary votages on the same side, I'd expect clearances to be to IEC-60950-1
it very quickly gets confusing. c
Agreed - BS 7671 does NOT apply to pre-manufactured assemblies, which should comply with appropriate standards (Regulation 113.1).
BS EN 62368-1 (IEC 62368-1) supersedes BS EN 60950-1 (IEC 60950-1) and BS EN 60065, both of which are due to be withdrawn this year.
Of course you can fit transformer in a CU. But unless the bellwires at 12 V or whatever coming out are over-sleeved to a standard that can hold off mains, you should really bring the ELV out in mains flex.