Induction Hob and Oven.

Supply P.M.E. Ze=0.28 Ohms. Cooker circuit, 5m long, 6.00mm2 T&E. Small bungalow. Cooker circuit protected by a B32 M.C.B. and 30mA R.C.D.


Induction hob recommended to be protected by a 20 Amp M.C.B. for full power setting. Wired in 5 core manufacturers' HO5 flex. L and N cores connected in pairs of 1.5mm2 conductors. C.P.C. single 1.5mm2 core.


Oven rated at 13 Amps but 16 Amps when in very hot self cleaning mode. Manufacturers' flex is 1.5mm2 3 core.


Both appliances are connected to the 32 Amp cooker circuit.


Can 433.3.1 (ii) be applied?


Thoughts?


Is fault protection adequate?


Thanks,


Z.




Parents
  • The fault protection is perfectly adequate Z, the cables are perfectly adequately rated for the expected load, but your only possible snag could be the manufacturers instructions. Do they say a minimum 20A CPD or a maximum 20A CPD? I expect that they do not say either, and the hob takes more than 16A at full power (that is why it has a 3mm2 cable) and I would not be surprised if it takes more than 20A, so the next size up is 32A. I also assume that the instructions do not say the appliance needs 2 supplies, so a 32A circuit is obvious, otherwise the oven and hob together may run into tripping of a 20A CPD. Please explain why you are panicking?
Reply
  • The fault protection is perfectly adequate Z, the cables are perfectly adequately rated for the expected load, but your only possible snag could be the manufacturers instructions. Do they say a minimum 20A CPD or a maximum 20A CPD? I expect that they do not say either, and the hob takes more than 16A at full power (that is why it has a 3mm2 cable) and I would not be surprised if it takes more than 20A, so the next size up is 32A. I also assume that the instructions do not say the appliance needs 2 supplies, so a 32A circuit is obvious, otherwise the oven and hob together may run into tripping of a 20A CPD. Please explain why you are panicking?