This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Induction Hob and Oven.

Supply P.M.E. Ze=0.28 Ohms. Cooker circuit, 5m long, 6.00mm2 T&E. Small bungalow. Cooker circuit protected by a B32 M.C.B. and 30mA R.C.D.


Induction hob recommended to be protected by a 20 Amp M.C.B. for full power setting. Wired in 5 core manufacturers' HO5 flex. L and N cores connected in pairs of 1.5mm2 conductors. C.P.C. single 1.5mm2 core.


Oven rated at 13 Amps but 16 Amps when in very hot self cleaning mode. Manufacturers' flex is 1.5mm2 3 core.


Both appliances are connected to the 32 Amp cooker circuit.


Can 433.3.1 (ii) be applied?


Thoughts?


Is fault protection adequate?


Thanks,


Z.




Parents
  • The manufacturer's instructions for the last hob I installed required a 25A "fuse" - not min or max, but exactly.
Reply
  • The manufacturer's instructions for the last hob I installed required a 25A "fuse" - not min or max, but exactly.
Children
No Data