I wonder if any of you guys would have any idea of the electrical demand for the pumps for a water mist sprinkler system? Five floors, with the ceiling of the top floor being about 25m above the tank in the basement. Each storey is around 400m2. I know that it is a bit of a daft question but we are on our limit with maximum demand and will probably have to put the pumps on a priority arrangement. I just want to get a heads up An inkling would do.
My neighbour has a water mist system in his house. The same firm that installed it does an annual service. After 3 or four years of servicing the firm failed the system because the MCB of the pump circuit was a B-type and it needed to be C-type. So if it needed to work at any time prior to this, it probably wouldn't have.
My neighbour has a water mist system in his house. The same firm that installed it does an annual service. After 3 or four years of servicing the firm failed the system because the MCB of the pump circuit was a B-type and it needed to be C-type. So if it needed to work at any time prior to this, it probably wouldn't have.