davidwalker2:
My own UFH system is wet. It comprises concrete slab, insulation, UFH tubing, engineered wood floor. It is driven directly from a combi boiler, the boiler water i.e. the UFH water, cycles between 35 degrees C and 45 degrees C, the thermal inertia of the floor smooths this out and the floor is pleasantly warm to the foot, probably around 38 - 39 degrees.
That's incredibly hot for UFH - BS EN 1264 Part 2 provide maximum foot comfort temperature of 29°C for living areas and 33°C for wet rooms
OMS
davidwalker2:
My own UFH system is wet. It comprises concrete slab, insulation, UFH tubing, engineered wood floor. It is driven directly from a combi boiler, the boiler water i.e. the UFH water, cycles between 35 degrees C and 45 degrees C, the thermal inertia of the floor smooths this out and the floor is pleasantly warm to the foot, probably around 38 - 39 degrees.
That's incredibly hot for UFH - BS EN 1264 Part 2 provide maximum foot comfort temperature of 29°C for living areas and 33°C for wet rooms
OMS