SWA in U/F floor slab

Got a job where a new submain - approx 25 metre run in 16mm 3 core SWA. Embedded directly into a new concrete floor where wet U/F heating will be installed. Am trying to work out the best order of installation - that is, should the cable go in first, then the insulation, followed by the U/F pipework,and finally followed by the slab. Am not sure what order the u/f heating side will be installed and am also thinking about how if any correction factors may need to be applied for the current carrying capacity. I have sized the cable with a little overhead in mind in terms of actual final demand, but am still a little concerned about final slab operating temperature

Comments welcome.

PS - Am not liking this new format - it is like writing inside a letterbox when compiling posts!
Parents
  • sounds like there will be a concrete slab, then insulation, then ufh coils clipped to the insulation then a screed poured. The cable would live very nicely in the concrete slab no problems. The screed will have perimeter insulation fitted, so running it in the screed at the edge will make little difference to heat loss of the cable.
Reply
  • sounds like there will be a concrete slab, then insulation, then ufh coils clipped to the insulation then a screed poured. The cable would live very nicely in the concrete slab no problems. The screed will have perimeter insulation fitted, so running it in the screed at the edge will make little difference to heat loss of the cable.