"17 edition"consumer units still being sold.

After watching a webinar describing the dangers of using dual rcd cu,s with type AC rcd supplying dishwashers,induction hobs etc,

I was wondering why,more than 12months after 18th came into force,they are still for sale.Thanks for any opinions.

                                                                                                          Regards,Hz

Parents
  • Andy are you suggesting that a short to case after a rectifier makes a DC fault?

    No, I'm suggesting the fault current will be something other than a pure sine-wave.

     
    First the fault current available is on average half the PSSC

    An earth fault on a TT system? I very much doubt that.

     
    This will not trip the CPD I suppose!

    Yes, I very much doubt that a overcurrent CPD will trip on a earth fault of any kind on a TT system.

     
    Also it is not a DC fault, hence my comment above about smooth and continuous DC, because a single rectifier will give an AC fault current which WILL operate the RCD.

    Again I suggest you look at Fig A53.1 - according to row 3 a half wave rectified earth fault current is NOT guaranteed detectable by an AC type.


       - Andy.
Reply
  • Andy are you suggesting that a short to case after a rectifier makes a DC fault?

    No, I'm suggesting the fault current will be something other than a pure sine-wave.

     
    First the fault current available is on average half the PSSC

    An earth fault on a TT system? I very much doubt that.

     
    This will not trip the CPD I suppose!

    Yes, I very much doubt that a overcurrent CPD will trip on a earth fault of any kind on a TT system.

     
    Also it is not a DC fault, hence my comment above about smooth and continuous DC, because a single rectifier will give an AC fault current which WILL operate the RCD.

    Again I suggest you look at Fig A53.1 - according to row 3 a half wave rectified earth fault current is NOT guaranteed detectable by an AC type.


       - Andy.