"17 edition"consumer units still being sold.

After watching a webinar describing the dangers of using dual rcd cu,s with type AC rcd supplying dishwashers,induction hobs etc,

I was wondering why,more than 12months after 18th came into force,they are still for sale.Thanks for any opinions.

                                                                                                          Regards,Hz

  • AJJewsbury:
    Whilst what he says is correct, DC leakage is not a normal phenomenon in installations. We have discussed it in car charging at length because there it is possible due to the car communications system with the charger and a single fault, but it is probably not possible with other electronic loads which never leak DC because the design runs with AC! Asymetric AC and other things do not result in DC (and it needs to be pure and smooth) leakage.

    I suspect problem is a bit wider than just AC type RCDs being blinded by pure d.c. Have a look at Figure A53.1 in the regs (page 192) - and then imagine a fault in an appliance from L after some of those diodes to the metallic case - especially on a TT system were we can't rely on the earth fault current being sufficient to trigger overcurrent protective devices or even blow the rectifier to smithereens. Then look at the right most column and note how quickly AC types disappear from the list of acceptable types.


        - Andy.


    Could there be a case for supplying those loads (or at least the mains' rectified part of the appliance) containing diodes through double wound isolating transformers to prevent R.C.D. blinding in case of earth faults?


    Z.


     


  • I may be a bit naïve here, but isn't the purpose of BS 7671 to ensure that the fixed wiring is safe?


    If an appliance poses a risk with a normal type AC RCD, then that should be a matter for the manufacturers to address.


    Either that or give a warning: "THIS APPLIANCE MUST NOT BE USED WITH A TYPE AC RCD. Purchasers should note that in order to comply with this advice, it may be necessary to have a new consumer unit fitted."


    That should be good for sales!
  • Chris Pearson:

    I may be a bit naïve here, but isn't the purpose of BS 7671 to ensure that the fixed wiring is safe?


    If an appliance poses a risk with a normal type AC RCD, then that should be a matter for the manufacturers to address.

     


    Yes, if an appliance affects the essential safety operation of an installation's R.C.D.(s) when required, it causes a risk for the whole or a large part of that installation if a split load consumer unit is used. The appliance is introducing a hazard and should not be used. Is there a regulation that covers this scenario, such as 133.1.1 etc?


    Z.


  • B.S. 7671 does require the use of Type B R.C.D.s in certain circumstances such as in certain solar supply systems.


    712.411.3.2.1.2.

    http://www.doepke.co.uk/rcd/images/RCD-B-types.pdf


    Z.


  • Thanks (the mention of regulations for type-B).  That type, I know, is sometimes required. My particular interest is more whether the latest regulations put hard requirements on using A instead of AC in almost every situation nowadays.


    "DC":  this causes plenty of confusion, as people use different meanings. One is pure DC: a constant value over multiple AC cycles, possibly arising 'gently' so as not to cause any trip. Another is that the mean value isn't zero, or (more extremely) that it's always in one direction like a half-wave rectified current, which is a form of "pulsating DC" in the words of RCD standards. 


    The distinction between type-AC and type-A is about responding to pulsating DC such as half-wave rectified current.  Pure DC is not the issue: it could affect either of these types according to the standard, as they're only required to tolerate the 6 mA steady DC level.   Handling even pure DC is the feature of type-B.


    It is not reliably true that a type-AC will operate with half-wave rectified current (pulsating DC) even if this is made, say, twice the normal rated value.  It might operate.  Or it might not operate even with multiple amps flowing. It depends on the design.  Don't be too confident based on an example measurement.  I've seen more variation between type-AC than type-A.  In the best case, a type-AC basically seems to be type-A under another label.  In the worst case a 30 mA type-AC can permit amps of "pulsating DC" without tripping, at least in one direction.  It depends on the design details, which can vary a lot within the bounds placed by the standard. See the final paragraph.


    The non-tripping of type-AC with half-wave rectified current is worrying because: tripping can fail even with high currents; and the type of fault is not at all so improbable (in my estimation) as some others that could make pure DC; and UK systems sometimes rely on the RCD for ADS.  I consider that worse than the type-A vs type-B issue, since a type-A with big enough AC fault current (compared to any pure DC current) does trip, according to all my tests; being made less sensitive is not desirable, but it's better than being anaesthetised.


    A TT earth electrode in a system with 30 mA type-AC RCD could well have a resistance of 20 ohms.  That would limit the current through a L-PE fault in a diode to be a value that the diode in a larger device could tolerate and that wouldn't trip an OCPD.  One could say similarly for a diode in a smaller device with a higher electrode resistance, e.g. 80 ohms (still plausible).  But the potential on all the PE relative to (real)earth would be half-wave ~230 V, unless source earthing were also weak.  As said above, some type-AC RCDs would actually respond to this, but some wouldn't: they're not required to.  I consider this a higher risk than some other dangers for which special RCDs and other special measures are pushed.  The good reliability of many appliances is one saving grace: having any fault, let alone through a diode, is very unusual.


    In case anyone wants to understand how a 30 mA RCD (type AC) can manage fail to operate even on e.g. 30x  I_{\\delta n} of half-wave rectified current, here's a quick explanation.  Take a current-transformer with magnetically hard material (cheap), as is typical of a true type-AC RCD.  Start applying the current.  As the current moves away from zero, the core becomes magnetised in this direction, and likely goes into saturation if the residual current is well above its rating. The non-saturated relative permeability of RCD cores is pretty high - tens of thousands - so losing most of this during saturation means there's relatively negligible change of flux. And when the current comes down near to zero again, the hardness of the core prevents the flux going down much either, when there isn't any reversal of the current (as with real AC) to push the magnetization the other way.  So the change of flux after that first few milliseconds is really very small, whereas with full-wave AC it would be much more.  On the first edge of the current away from zero there's a chance of tripping as the flux goes between zero and saturation, but usually only for one direction of the current!  That's because the sensitive trip-mechanism of non-powered RCDs normally uses a permanent magnet to hold a magnetic circuit closed, and a coil to demagnetise this magnetic circuit: one direction of the induced current demagnetises, and the other doesn't.  (That's why, on type-A too, you can often see a ~10 ms change in trip time when varying between 0 and 180 degrees. With some types of powered RCDs this dependence can be avoided.)   I've recently started a set of measurements on RCDs that I've had planned for some months: as promised once before, I will soon put up a webpage of results, along with the actual device models.


  • Andy are you suggesting that a short to case after a rectifier makes a DC fault?

    No, I'm suggesting the fault current will be something other than a pure sine-wave.

     
    First the fault current available is on average half the PSSC

    An earth fault on a TT system? I very much doubt that.

     
    This will not trip the CPD I suppose!

    Yes, I very much doubt that a overcurrent CPD will trip on a earth fault of any kind on a TT system.

     
    Also it is not a DC fault, hence my comment above about smooth and continuous DC, because a single rectifier will give an AC fault current which WILL operate the RCD.

    Again I suggest you look at Fig A53.1 - according to row 3 a half wave rectified earth fault current is NOT guaranteed detectable by an AC type.


       - Andy.
  • If you have a look to see what is gone on mainland Europe you will find they’re the equivalent of a dual RCD consumer unit with one split protected by a type AC RCD supplying lighting etc and the other with a type A supplying the EV charger, hob and washing machine.


    Is it typical the traditional British trait of going over the top showing through with type A RCDs being used for all circuits?


    Andy Betteridge
  • In terms of costs, a Type A RCBO can now be had for around £12+VAT from CPFUSEBOX, so no excuses there on a costs basis. These are even cheaper than a Hager or Wylex branded Type AC item.

    About a year ago, I paid just over £100 for a Chint Type B 2 pole 80A RCD for a GSHP set up as recommended by the heat pump manufacturer.

    Hager wanted around £300+ for the same item, and Dpoeke wanted £700!


    Perhaps a better way of looking at it might be - Is having a type AC RCD worse then having no RCD at all?
  • If you have a look to see what is gone on mainland Europe you will find they’re the equivalent of a dual RCD consumer unit with one split protected by a type AC RCD supplying lighting etc and the other with a type A supplying the EV charger, hob and washing machine.

    Is it typical the traditional British trait of going over the top showing through with type A RCDs being used for all circuits?


    I don't think it is in this case (over the top).  When you say "mainland Europe" you perhaps are thinking of France (or Italy?).  In Germany and Sweden (and, if it follows the usual pattern, most/all others with German/Scandinavian languages) the type AC has not been used in some decades.   Rather strangely, this means there's a correlation between having extensive use of TT systems and permitting use of type-AC - the opposite correlation would be easier to understand, due to the typical dependence of TT ADS on the RCD.


    My price comparisons last summer suggest that A would be cheaper in the UK if one didn't use AC. This is based on comparing prices between countries that do or don't still allow type-AC: when type-A is a special thing just for the few who bother to think and ask, it's more expensive; or to put it another way, if you have both, without any other difference, the A should cost more if there's to be any reason for having the AC at all.  And looking at ready-made CUs in the UK, or at many retailers' RCD selections, it's just obvious that the flexibility of the UK regulations is abused: CUs commonly have purely type-AC for the one or two RCDs covering all circuits.


    Admittedly, if you were to push me to show a single case of a death due just to RCD type, I wouldn't be able to point to such a case. Anyone?  It does rather surprise me, in millions of TT installations.


  • Andy, why are you picking on TT installations? Have you a statistic that says that they cause deaths, and in how many cases is this due to RCD failure and how many due to some fault which you have yet to describe? Setting up a straw man is a common way used by troublemakers and charletons to show that the straw man is a problem, whereas such is not required if a real problem is identified. It is common in USA politics. I would be most interested to see the data, which is always missing with such arguments. I was not specifically talking about TT, just any installation, it is true that there could be special problems with certain faults on TT systems, which have never been as robust as TN-S or properly working TNC-S.


    Moving on to other ground, I do not really see why there is a significant difference between a type A and B in price, except that quantities may be smaller for Bs. They are undoubtedly electronic (as is the type AC I was testing recently) but this is not really a difference affecting price much. Volume electronics is very cheap to manufacture, the price paid is hardly related to the costs, for example Apple products and the cash mountain. The design of a DC sensitive RCD is not difficult anyway, although it probably would not have a transformer, just some precision electronics, perhaps some Hall sensors and coreless coils. The chip to do this would cost perhaps 20p in million quantities, and you could have it in less than a year. Seeing the problems smart meters have had, it is fairly obvious that the industry involved does not have the Engineers or technology available for such development work in what they consider an alien area. Certainly until they have the right product at the right price we should not change BS7671, there is no data that it is necessary or economic. I can just see all those EICRs saying code 1 for "the wrong type" of RCDs, based on the same "what if" statements unsupported by evidence.