Lightning conductor for ametuer radio antenna mast - electrician says regular PVC sheated yellow green wire is ok from mast to earth rod

Former Community Member
Former Community Member
As per title I am getting a corner of my house setup as a radio shack and wanted to protect it appropriately.

The antenna is made of fibre glass but sits on an aluminium pole that brings the total height to 10m tall (only house in the area).


We have agreed to setup an earth rod below the antenna mast and earth it but the question is - will regular 35mm green/yellow sheated earth be good enough to provide earthing for antenna mast while being exposed to the elements? How long will it last?


Any thoughts on the electrical setup for the radio? We are planning to use the same earth rod and make a TT island for the power socket that feeds the radio unit (as main electrics is PME). The radio will be fed electric connection through an MCB by taking power from the main distribution box protected by a Type 1/2/3 SPD (I have 3 phase 100A supply from DNO) and we will use the earth rod for earth supply.


The radio unit will be powered by a seperate consumer unit which gets it's earth supply from the rod (I might also get a Type 1 SPD in the TT island consumer box).


The antenna and the TT island powering the radio will be linked by a 700A rated earth bar enclosed outside the property in an IP65 enclosure.


Appreciate any thoughts on my setup.
Am I being overkill and do not need a TT island for my radio setup? Will earthing the antenna be sufficient?
Parents
  • will regular 35mm green/yellow sheated earth be good enough to provide earthing for antenna mast while being exposed to the elements? How long will it last?

    BS 7671 lists bare 25mm² copper as being sufficient for a buried earthing conductor for protection against both mechanical damage and corrosion (table 54.1)  - so you should be more fine with 35mm² PVC covered on that score. (Copper water pipes seem to survive the elements both buried and above ground almost indefinitely.)


    If it's to be used as a lightning conductor though it'll have to survive lightning currents - others here will know more about that than me.


     
    a corner of my house setup as a radio shack

    I'd be a bit wary of converting a part of the house to TT while keeping the remainder as TN. When you have two different earthing systems it's imperative to keep them out of reach of each other - otherwise there can be a significant shock risk between items of metalwork connected to the two different systems. Metallic plumbing systems are one obvious way the boundaries between the two systems can be crossed (both initially and future channges) - but even things like Class I portable appliances and/or extension leads risks reducing the distance between the two systems in a way the electrical designer can't really guard against. I'll let the 'ham' types on here suggest the best solution to that problem though.


        - Andy.
Reply
  • will regular 35mm green/yellow sheated earth be good enough to provide earthing for antenna mast while being exposed to the elements? How long will it last?

    BS 7671 lists bare 25mm² copper as being sufficient for a buried earthing conductor for protection against both mechanical damage and corrosion (table 54.1)  - so you should be more fine with 35mm² PVC covered on that score. (Copper water pipes seem to survive the elements both buried and above ground almost indefinitely.)


    If it's to be used as a lightning conductor though it'll have to survive lightning currents - others here will know more about that than me.


     
    a corner of my house setup as a radio shack

    I'd be a bit wary of converting a part of the house to TT while keeping the remainder as TN. When you have two different earthing systems it's imperative to keep them out of reach of each other - otherwise there can be a significant shock risk between items of metalwork connected to the two different systems. Metallic plumbing systems are one obvious way the boundaries between the two systems can be crossed (both initially and future channges) - but even things like Class I portable appliances and/or extension leads risks reducing the distance between the two systems in a way the electrical designer can't really guard against. I'll let the 'ham' types on here suggest the best solution to that problem though.


        - Andy.