Lightning conductor for ametuer radio antenna mast - electrician says regular PVC sheated yellow green wire is ok from mast to earth rod

Former Community Member
Former Community Member
As per title I am getting a corner of my house setup as a radio shack and wanted to protect it appropriately.

The antenna is made of fibre glass but sits on an aluminium pole that brings the total height to 10m tall (only house in the area).


We have agreed to setup an earth rod below the antenna mast and earth it but the question is - will regular 35mm green/yellow sheated earth be good enough to provide earthing for antenna mast while being exposed to the elements? How long will it last?


Any thoughts on the electrical setup for the radio? We are planning to use the same earth rod and make a TT island for the power socket that feeds the radio unit (as main electrics is PME). The radio will be fed electric connection through an MCB by taking power from the main distribution box protected by a Type 1/2/3 SPD (I have 3 phase 100A supply from DNO) and we will use the earth rod for earth supply.


The radio unit will be powered by a seperate consumer unit which gets it's earth supply from the rod (I might also get a Type 1 SPD in the TT island consumer box).


The antenna and the TT island powering the radio will be linked by a 700A rated earth bar enclosed outside the property in an IP65 enclosure.


Appreciate any thoughts on my setup.
Am I being overkill and do not need a TT island for my radio setup? Will earthing the antenna be sufficient?
Parents
  • you do not say how your antenna connects to the radio - many designs of ATU are in effect double wound RF transformers.

    There are 2 very distinct issues here -

    1) earthing PME/TT, and in your shoes I'd look to island as you propose if it is practiacl to keep TT earth and mains earth things apart (but beware of random items like radiators bringing  the PME earth into the shack room). But at install time you need to know the earth impedance, and it may be worth making provision to be able to monitor the voltage between the 2 earths.

    The other thing you can do to reduce risk, is simply to unplug the rig from mains, when not in use, breaking the earth as well as L and N, and especially when working on the antennas, and if you are not a heavy user, and do not operate when the mains voltage is misbehaving, that may well be all that is required really, and just use the PME earth for operation in a non-lightning state and when no-one is near the antennas - I'd like to think you'd not be transmitting then anyway.


    2) Lightning.

    Nothing you can do will protect against a direct strike, just insure and minimise the risk as best possible.

    Even a 10 ohm electrode will come up to 100kV plus during a modest 10kA strike - that will sideflash about 4 inches to any easier path, a megavolt will jump perhaps a metre or so.

    I tend to just drive the end of the mast into the ground - or a length of scaff pole beside it, but less than 10 ohms is a hard target to achieve.

    Induced voltages from strikes in the vicinity are more likely, but the voltages induced vary from nothing up to kV. Gas discharge devices accross the feeder or in a delat between feeder and ground help clip some of that. You need to select the voltage rating to suit the transmitter power.

    The only truly safe radio in the thunderstorm is one that is not connected to an  antenna, so make provision to interrupt the antenna feeds by a large air gap and short them to the external ground when not in use - a removable coax link is often the easiest.

    If you wish, carry a rod from the grounded mast onwards above the antennas, so that (hopefully) the mast tip is the attractor, rather than your prized rig. However, lightning is fickle stuff.


    Others will offer varying opinions - there are as many answers as circumstances.


    73 de G7VZY
Reply
  • you do not say how your antenna connects to the radio - many designs of ATU are in effect double wound RF transformers.

    There are 2 very distinct issues here -

    1) earthing PME/TT, and in your shoes I'd look to island as you propose if it is practiacl to keep TT earth and mains earth things apart (but beware of random items like radiators bringing  the PME earth into the shack room). But at install time you need to know the earth impedance, and it may be worth making provision to be able to monitor the voltage between the 2 earths.

    The other thing you can do to reduce risk, is simply to unplug the rig from mains, when not in use, breaking the earth as well as L and N, and especially when working on the antennas, and if you are not a heavy user, and do not operate when the mains voltage is misbehaving, that may well be all that is required really, and just use the PME earth for operation in a non-lightning state and when no-one is near the antennas - I'd like to think you'd not be transmitting then anyway.


    2) Lightning.

    Nothing you can do will protect against a direct strike, just insure and minimise the risk as best possible.

    Even a 10 ohm electrode will come up to 100kV plus during a modest 10kA strike - that will sideflash about 4 inches to any easier path, a megavolt will jump perhaps a metre or so.

    I tend to just drive the end of the mast into the ground - or a length of scaff pole beside it, but less than 10 ohms is a hard target to achieve.

    Induced voltages from strikes in the vicinity are more likely, but the voltages induced vary from nothing up to kV. Gas discharge devices accross the feeder or in a delat between feeder and ground help clip some of that. You need to select the voltage rating to suit the transmitter power.

    The only truly safe radio in the thunderstorm is one that is not connected to an  antenna, so make provision to interrupt the antenna feeds by a large air gap and short them to the external ground when not in use - a removable coax link is often the easiest.

    If you wish, carry a rod from the grounded mast onwards above the antennas, so that (hopefully) the mast tip is the attractor, rather than your prized rig. However, lightning is fickle stuff.


    Others will offer varying opinions - there are as many answers as circumstances.


    73 de G7VZY