8 metre meter tails

Hello All,

Scenario is; conversion of basement with a 3P supply to 3 separate flats. TNCS. To get a new CU into the furthest flat I've proposed 25mm singles in Scottish Power red conduit. The conduit would be run in the correct zone in a void about 100mm above a plasterboard ceiling with no insulation at this point. I get the max current to 80A for this method and a fused switch would be installed at the origin after the DNO cut out Have I missed anything here? I'd assume to measure volt drop to the origin and disconnection times to the CU as per.

Thanks for your time,

Pete
Parents
  • So yes, at the origin, and it's not possible to install an 80A switched fuse after the cutouts to protect the run to the the CU?

    Thanks for your time
Reply
  • So yes, at the origin, and it's not possible to install an 80A switched fuse after the cutouts to protect the run to the the CU?

    Thanks for your time