Chris Pearson:
I don't doubt for one minute the expertise of Mike, Dave, and OMS, but this all seems to be OTT. Just how are scanners put into a ship or a field hospital?
Reasonably easily - the source impedance requirements aren't that difficult to achieve. Back in the day, even the sockets used for mobile x-ray had impedance limits - most of this stuff has been in HTM documentation for many decades.
As the OP indicated, the CT will still work, just that you get ever increasing image degradation - which is then exacerbated if you need to share those images over networks resulting in further degradation
To get this into context, in a modern acute hospital of say 500 beds, it wouldn't be unreasonable to have a firm 4MVA supply capability (so essentially 8MVA depending on how the source transformers are configured for A+B primary and secondary supplies into the Healthcare estate)
Most hospital electrical loads are disturbing to some extent, so sensible design is needed in terms of what you try and do. It's never that sensible to have your main diagnostic capability as far away from your supply as possible - usually you would design for the opposite. There are a few idiotic cases such as where a know nothing project manager decided that installing a new MRI scanner in a room directly above a set of transformers was perfectly reasonable - the magnetic field of the MRI sweeping through the transformers resulted in some interesting disturbance issues - ohh how we laughed.
The above aside - 0.06 Ohm limit is only roughly 4% voltage drop in a cable - so it's hardly unreasonable assuming you have decent transformers in place, and noting this is a swap out rather than an additional scanner.
Regards
OMS
LV Panel - Supply
L1 - N = 6.19kA (For 3-phase condition √3 x 6.19kA = 10.72kA)
John Peckham:
OMS
Is this line impedance the impedance of one line conductor or 2 line conductors?
I know the top man in the country for Medical Locations. I will see if I can get him to comment on this post.
Well, typically HTM 06-01 indicates that it is measured between one or more lines as required. Obviously, depending on the source of the equipment, manufacturers may state specific requirements (eg, some GE kit may be assuming a delta supply source)
I can't specifically state that, John - read the instructions would be good advice.
Regards
OMS
To get a closer actual measurement in the field measure the fault current phase to phase with a decent loop tester and divide the reading by 0.87.