statter:
Thanks Z.
No, I think outbuilding 1 is effectively TNC-S and not TT (the TT earth is not connected).
I think my concern is that the path that the earth conductor for outbuilding 1 follows is different to the path that the L &N conductors follow.
Having said that the diagram provided is very helpful for anyone who wants to know what the earthing arrangements are.
The fact that a TNC-S earthed installation is down stream (in L&N conductor terms) of a TT earthed installation is also at the very least unusual. This wouldn't normally arise as the installation of the separate earth would be not much easier than the installation of a separate supply (E&L&N). In this case I suspect that the separate earth was originally an extra bonding conductor and has been repurposed, but I may be wrong.
Yes, I would think that the 10.0mm2 G/Y single cable was originally a main bonding conductor for the metal gas pipe in outbuilding 1. It is normally the case that the supply L and N take the same route as the associated C.P.C. so I can see where the confusion comes in here. Electrically if the supply is just P.M.E. in building 1 with its associated earthing then all should be safe. We don't really want two earthing systems within the same building. If sufficient in size a cable can be a combined bonding conductor and C.P.C. at the same time.
Z.
statter:
Thanks Z.
No, I think outbuilding 1 is effectively TNC-S and not TT (the TT earth is not connected).
I think my concern is that the path that the earth conductor for outbuilding 1 follows is different to the path that the L &N conductors follow.
Having said that the diagram provided is very helpful for anyone who wants to know what the earthing arrangements are.
The fact that a TNC-S earthed installation is down stream (in L&N conductor terms) of a TT earthed installation is also at the very least unusual. This wouldn't normally arise as the installation of the separate earth would be not much easier than the installation of a separate supply (E&L&N). In this case I suspect that the separate earth was originally an extra bonding conductor and has been repurposed, but I may be wrong.
Yes, I would think that the 10.0mm2 G/Y single cable was originally a main bonding conductor for the metal gas pipe in outbuilding 1. It is normally the case that the supply L and N take the same route as the associated C.P.C. so I can see where the confusion comes in here. Electrically if the supply is just P.M.E. in building 1 with its associated earthing then all should be safe. We don't really want two earthing systems within the same building. If sufficient in size a cable can be a combined bonding conductor and C.P.C. at the same time.
Z.