davezawadi:
This is very very unlikely to cause loss of life Z. The backbox or fuse enclosure or whatever is Earthed exactly so that if a conductor contacted it would trip/blow the CPD. Much more likely is threading T&E through holes in walls and inadequate fixings so that it rubs WITH MOVEMENT during the installation life. You really ought to get a degree of realism here and stop stressing yourself unnecessarily as death will be closer than you think due to heart or brain problems. Just relax a little! Perhaps the staying in and watching youtube is getting to you, why not try testing every RCD you have with some added DC and letting me have the results, it is quite a long job?
The video clip emphasises the need to attend to detail to prevent danger. Did you watch it? If not then you do not have the complete picture.
I agree that a chaffed cable may not lead to death directly, but if it leads to a loss of supply then who knows what may happen if essential equipment is disconnected. You have missed the point of my post entirely.
Z.
lyledunn:
Rose park Care Home January 2004. Fourteen dead. Ignition source; arcing where cable passed through knockout in distribution board. No grommet fitted.
Of course as the introduction to the video indicates, it normally takes a series of things to go wrong. Nonetheless, rare as it might be, really important to properly secure cables and protect them as they pass through knockouts to guard against potential arcing.
The fire started in a cupboard along a corridor, following an electrical fault. It is thought that aerosols stored in the cupboard exploded, the force of the blast blowing open some nearby fire doors along the corridor. Materials immediately outside the cupboard – chairs, wallpaper, timber handrails – ignited, causing heat and smoke to spread.
A terrible avoidable tragedy.
Z.