Electrical Safety Standards in the Private Rented Sector (England) Regulations 2020.

So I posted this on a lively Facebook group and got every view under the sun.



‘Anyone been asked to do an EICR in accordance with the new law for rented properties yet? 



(I know it’s not until 1st June 2020 or 1stApril 2021)



All private rented properties in England must fully meet the 18th edition. No Codes. No deviations. 



http://www.legislation.gov.uk/uksi/2020/312/contents/made



The general consensus was if it affects me then C3’s remain acceptable. 



If it does not affect me no deviations are allowed.



My view, as someone who does virtually no domestic is two fold, 



1; The Law is badly written. 



2; The Law requires installations to actually meet the 18th (unamended) 



The Housing Act 2004 calls for installations to be ‘safe for continued use’, this new Act no longer uses that language instead it says



The Act



3.—(1) A private landlord(1) who grants or intends to grant a specified tenancy must—



(a)



ensure that the electrical safety standards are met during any period when the residential premises(2) are occupied under a specified tenancy;



(b)



ensure every electrical installation in the residential premises is inspected and tested at regular intervals by a qualified person;



Definitions in the Act



“electrical safety standards” means the standards for electrical installations in the eighteenth edition of the Wiring Regulations, published by the Institution of Engineering and Technology and the British Standards Institution as BS 7671: 2018.



Now, The 18th, and indeed most versions have wording similar to this In part 6



Existing installations that have been installed in accordance with earlier editions of the Regulations may not comply with this edition in every respect. This does not necessarily mean that they are unsafe for continued use or require upgrading.



Clearly, This is intended to prevent mandatory upgrading and retain the fact that regulations are not retrospective and never have been. 



However, This law does not call for ‘Satisfactory’ or ‘Safe for continued use’ it calls for ‘ensure that the electrical safety standards are met’ 



A code, by any definition indicates a non compliance, and, surely a non compliance by definition indicates a standard has not been met. 



And then there is ‘Qualified’



“qualified person” means a person competent to undertake the inspection and testing required under regulation 3(1) and any further investigative or remedial work in accordance with the electrical safety standards; 



This would seem to preclude non certificated members of QS schemes and actually require that the individual indeed qualified? 



It is a mess really.


Parents
  • If anyone wants a copy of my updated standard specification for carrying out a domestic periodic inspection I happy to email you a copy.


    It is designed for contractors to send to their clients before they do the inspection so that it is clear what they are going are going to do and meets the requirement for the inspector to agree the extent and limitations before starting work.


    In addition landlords can use it to issue to contractors to specify what they want.


    Just emial on info@atutetechnicalservices.co.uk for a copy.
Reply
  • If anyone wants a copy of my updated standard specification for carrying out a domestic periodic inspection I happy to email you a copy.


    It is designed for contractors to send to their clients before they do the inspection so that it is clear what they are going are going to do and meets the requirement for the inspector to agree the extent and limitations before starting work.


    In addition landlords can use it to issue to contractors to specify what they want.


    Just emial on info@atutetechnicalservices.co.uk for a copy.