kA^2s

This is not something I need answered: I already have a view - although someone might manage to change it. It's hoped to be a quiz-like stimulus to think about caution with units and prefixes. A comment here a week or two ago prompted me to look again in a standard - this time IEC61008-1 (2010). There I noticed a table of peak currents Ip and 'let through' I2t, that the devices are tested with. Here's a small excerpt,

81e202a88c2cf17c4a84e9cec5efcc52-huge-ka2s.png


The columns give test values for RCDs that have rated currents 16 A and 20 A and with rated withstand of 6 kA 'prospective'. (The low Ip values are reasonable if the RCD is expected to be protected by a current-limiting device rated close to its own rated current In.) 


It seems that the unit they give for I2t is used in a way I've also seen in one manufacturer's specifications for MCBs/fuses.
But is this 'correct'?  

A comparison to mm^2 might be helpful. 



The login process reminded me of another question that often occurs when seeing the IEE building, or logging into a 'thexxx.org' website: nearly 20 years on, is there anyone who sees a benefit of the change from IEE to THEIET? Too late now, in any case. One can hope the name doesn't make too much difference to what happens either way, although I feels the lack of mention of electricity is a bit strange for the institution's current or past work. I wonder if the cynical view I had at the time of the vote was actually unjust. 

Parents
  • If the derived unit is A2s, then 1000 A2s = 1 kA2s
Reply
  • If the derived unit is A2s, then 1000 A2s = 1 kA2s
Children
No Data