Likely Gas Combi-Boiler P.C.B. Damage.

Mornin' all,

                         I hope that you are all keeping your spirits up during these trying times.


Yesterday I made a mistake. I can only attribute the reason to the work environment and me being pre-occupied with self distancing on site and being distracted by the house occupants, plus stupidity.


The owner had apparently struck a wall thermostat due to it being unreliable in operation, and he having a bad temper. The dial part was cracked. He asked me to change it for a new one. The wall thermostat is a Honeywell make. I have wired up many of these in my time. I did not have a Honeywell replacement but did have another make of a similar design. So I fitted that. After I had fitted the new one I noticed that I had no mains supply showing at the wall stat. I checked the switched fused connection unit at the boiler and it was displaying a glowing neon, so the 3 Amp fuse there was intact. I was asked to refit the original wall stat, which I did, and a gas engineer is coming out to look at the boiler. I did not see the boiler working initially, but the owner and his wife assured me that it was working that morning.


I must have wired the new wall stat up wrongly and shorted between L and N. That probably blew the 1, 2 or 3.15 Amp fuse on the boiler P.C.B. I did not dismantle the boiler to look.


What is the chance of irreparable damage to the boiler P.C.B?


Unfortunately I did not note the make and model of the boiler.


Bye,


Gloomy Z.

Parents
  • I would be a little surprised if the fuse in the boiler had gone and not taken out the 3a in the spur too.

    Also maybe the thermostat isn’t switching 230, it could be low voltage? I nearly got caught out by one of those last year...
Reply
  • I would be a little surprised if the fuse in the boiler had gone and not taken out the 3a in the spur too.

    Also maybe the thermostat isn’t switching 230, it could be low voltage? I nearly got caught out by one of those last year...