This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

Rcd discrimination

Any Information greatly appreciated.


Each outdoor socket has to be RCD protected, so if you have a junction box supplying more than one outdoor 30ma socket, how do you achieve RCD discrimination all the way back. I have an older C/U and the rcd on it is also 30ma?


A spur from internal plug to fused switch outside, which then feeds multiple outdoor sockets?


this is just a scenario I am trying to figure out.


thanks for anyone’s time.


Andy
Parents
  • If you have an RCD in the supply to the socket, either at the socket or back at the dis board, then the socket meets the regs, as it has RCD protection. The regs do not care about where.
Reply
  • If you have an RCD in the supply to the socket, either at the socket or back at the dis board, then the socket meets the regs, as it has RCD protection. The regs do not care about where.
Children
No Data