This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

TNCS Condition

f51b9c4342acb17854276ea4c05938ae-huge-7ffcd357-6382-406d-ba19-012100635c9e.jpg

Perhaps you can shed some light on this condition for TNCS systems in the Irish Rules. I can only see that as RE decreases RB becomes more onerous but to be honest I am not really getting the essence.
Parents
  • Lol.


    What we call the DNO earth is referred to as the DSO earth in figure 8.


    So in for a penny, in for a pound!


    If the DSO earth is 20 ohms the maximum consumer installation earth rod impedance is on the face of it is 5.26 ohms, but it is actually referring to the extraneous-parts, not the rod.


     Andy Betteridge
Reply
  • Lol.


    What we call the DNO earth is referred to as the DSO earth in figure 8.


    So in for a penny, in for a pound!


    If the DSO earth is 20 ohms the maximum consumer installation earth rod impedance is on the face of it is 5.26 ohms, but it is actually referring to the extraneous-parts, not the rod.


     Andy Betteridge
Children
No Data