This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

TNCS Condition

f51b9c4342acb17854276ea4c05938ae-huge-7ffcd357-6382-406d-ba19-012100635c9e.jpg

Perhaps you can shed some light on this condition for TNCS systems in the Irish Rules. I can only see that as RE decreases RB becomes more onerous but to be honest I am not really getting the essence.
Parents
  • I have it in mind that Uoc  is 240 volts despite the declared voltage being 230 volts.


    20 ohms would actually be high for RB and the lower it is the lower RE can be.


     Andy B.
Reply
  • I have it in mind that Uoc  is 240 volts despite the declared voltage being 230 volts.


    20 ohms would actually be high for RB and the lower it is the lower RE can be.


     Andy B.
Children
No Data