This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

EV CHARGING EQUIPMENT

I am hearing from my network of contractors, that have actually read the new 722, that they have been asking charging equipment manufactures for documentary proof to comply with Note 5 of 722.411.4.


They are getting knocked back for asking or in one case a Declaration that says the particular device complies with BS 7671. I think that is wrong to declare that as BS 7671 is an installation safety standard and not a product standard. I believe that as a minimum the equipment must comply with the Low Voltage Directive and be CE marked. I also believe that manufacturers have to issue a Declaration of Conformity. 


BS 7671 722 has numerous references to the various standards required such as BS EN 61851 that the equipment must comply with. I am thinking it may be illegal to offer the sale of equipment that does not comply with the Low Voltage Directive and is not CE marked?


I am hoping the countries top man of equipment safety standards, Paul Skyrme , sees this post and will come on and give us his expert view?


Has any forum member asked for a Declaration of Conformity from EV charging equipment manufacturers and received one?
Parents
  • Andy


    Down to the contractor I think as they should have provided an EIC that one or more individuals has designed the installation to BS 7671, installed the installation to BS 7671 and has been inspected and tested the installation for compliance with BS 7671 and those person(s) have certified compliance with their signatures.



    I would only FI an apparent non-compliance if I was unsure if the EV charging equipment was not compliant after I had made inquiries with the equipment manufacturer. Using an FI without making reasonable inquires because the inspector cannot make an effort is not exercising due diligence in my book.

Reply
  • Andy


    Down to the contractor I think as they should have provided an EIC that one or more individuals has designed the installation to BS 7671, installed the installation to BS 7671 and has been inspected and tested the installation for compliance with BS 7671 and those person(s) have certified compliance with their signatures.



    I would only FI an apparent non-compliance if I was unsure if the EV charging equipment was not compliant after I had made inquiries with the equipment manufacturer. Using an FI without making reasonable inquires because the inspector cannot make an effort is not exercising due diligence in my book.

Children
No Data