I am hearing from my network of contractors, that have actually read the new 722, that they have been asking charging equipment manufactures for documentary proof to comply with Note 5 of 722.411.4.


They are getting knocked back for asking or in one case a Declaration that says the particular device complies with BS 7671. I think that is wrong to declare that as BS 7671 is an installation safety standard and not a product standard. I believe that as a minimum the equipment must comply with the Low Voltage Directive and be CE marked. I also believe that manufacturers have to issue a Declaration of Conformity. 


BS 7671 722 has numerous references to the various standards required such as BS EN 61851 that the equipment must comply with. I am thinking it may be illegal to offer the sale of equipment that does not comply with the Low Voltage Directive and is not CE marked?


I am hoping the countries top man of equipment safety standards, Paul Skyrme , sees this post and will come on and give us his expert view?


Has any forum member asked for a Declaration of Conformity from EV charging equipment manufacturers and received one?
Parents

  • OlympusMons:




    Sparkingchip:
    A shaver socket gets an infographic and a label  which spoils it sleek design when it is going to be installed in a swish bathroom, but the it seems 13-amp EV sockets need to remain unblemished even though they are intended to be installed on a wall outside or within a garage and in the majority of installations are going to be covered with a lid to get the required IP rating; and labelling on the front of a USB charger built into a 13-amp plug socket is obligatory.


     



     

     

    There must also be a  label adjacent or on the front face stating "suitable for electric vehicle charging", 722.55.101.0.201.1 (I)


    On the front face? I'm sure BS 7671 Regulation 722.55.101.0.201.1 (i)  does NOT specify that the socket-outlet itself has the manufacturer's label "EV" on the front face !

    Clause 7.1 of BS 1363-2 says that the socket-outlet must be marked with the standard number "BS 1363", in 7. 1(b), and that if the socket-outlet is suitable for EV charging, "/EV" must follow it (in the same way that "BS 1363/A" is a portable socket-outlet). Such marking is usually provided, along with the voltage and current rating, on the rear.


    The difference from a normal socket-outlet to BS 1363-2 is that, for a BS 1363/EV socket-outlet, cyclic loadings tests are different, and there are special conditions for the breaking capacity and normal operational tests.


    However,722.55.101.0.201.1 does say that the installer should put a label on  the front face or, or near, the socket-outlet, unless there is no possibility of confusion, stating "Suitable for electric vehicle charging". This is for the user.


    The IET Code of Practice for EV Charging Equipment Installation, in Section 4.9, also recommends that a BS 1363/EV socket-outlet is labelled as such by the installer to help consumers understand which socket-outlet to use for their vehicle ... but this should only be done for BS 1363/EV socket-outlets fully installed in accordance with the CoP.


    In general, it is recommended that dedicated charging equipment (Mode 3 or Mode 4) is provided where practicable.

     



    I asked for one in my local merchant and they said never heard of it but can get one printed up, at a price.




    Well, hopefully my explanation above shows why

     

    It is not clear from the reg that using a sharpie and writing EV on the back of the faceplate of a normal bs1363-2 would not comply.



    The Regulation, along with the reference standard BS 1363-2, explains why a sharpie hand-mark on the rear would not do, and BS 7671 still requires a user instruction label on the front - this could be, at its simplest, printed from something like a standard label printing machine.

     

Reply

  • OlympusMons:




    Sparkingchip:
    A shaver socket gets an infographic and a label  which spoils it sleek design when it is going to be installed in a swish bathroom, but the it seems 13-amp EV sockets need to remain unblemished even though they are intended to be installed on a wall outside or within a garage and in the majority of installations are going to be covered with a lid to get the required IP rating; and labelling on the front of a USB charger built into a 13-amp plug socket is obligatory.


     



     

     

    There must also be a  label adjacent or on the front face stating "suitable for electric vehicle charging", 722.55.101.0.201.1 (I)


    On the front face? I'm sure BS 7671 Regulation 722.55.101.0.201.1 (i)  does NOT specify that the socket-outlet itself has the manufacturer's label "EV" on the front face !

    Clause 7.1 of BS 1363-2 says that the socket-outlet must be marked with the standard number "BS 1363", in 7. 1(b), and that if the socket-outlet is suitable for EV charging, "/EV" must follow it (in the same way that "BS 1363/A" is a portable socket-outlet). Such marking is usually provided, along with the voltage and current rating, on the rear.


    The difference from a normal socket-outlet to BS 1363-2 is that, for a BS 1363/EV socket-outlet, cyclic loadings tests are different, and there are special conditions for the breaking capacity and normal operational tests.


    However,722.55.101.0.201.1 does say that the installer should put a label on  the front face or, or near, the socket-outlet, unless there is no possibility of confusion, stating "Suitable for electric vehicle charging". This is for the user.


    The IET Code of Practice for EV Charging Equipment Installation, in Section 4.9, also recommends that a BS 1363/EV socket-outlet is labelled as such by the installer to help consumers understand which socket-outlet to use for their vehicle ... but this should only be done for BS 1363/EV socket-outlets fully installed in accordance with the CoP.


    In general, it is recommended that dedicated charging equipment (Mode 3 or Mode 4) is provided where practicable.

     



    I asked for one in my local merchant and they said never heard of it but can get one printed up, at a price.




    Well, hopefully my explanation above shows why

     

    It is not clear from the reg that using a sharpie and writing EV on the back of the faceplate of a normal bs1363-2 would not comply.



    The Regulation, along with the reference standard BS 1363-2, explains why a sharpie hand-mark on the rear would not do, and BS 7671 still requires a user instruction label on the front - this could be, at its simplest, printed from something like a standard label printing machine.

     