EV CHARGING EQUIPMENT

I am hearing from my network of contractors, that have actually read the new 722, that they have been asking charging equipment manufactures for documentary proof to comply with Note 5 of 722.411.4.


They are getting knocked back for asking or in one case a Declaration that says the particular device complies with BS 7671. I think that is wrong to declare that as BS 7671 is an installation safety standard and not a product standard. I believe that as a minimum the equipment must comply with the Low Voltage Directive and be CE marked. I also believe that manufacturers have to issue a Declaration of Conformity. 


BS 7671 722 has numerous references to the various standards required such as BS EN 61851 that the equipment must comply with. I am thinking it may be illegal to offer the sale of equipment that does not comply with the Low Voltage Directive and is not CE marked?


I am hoping the countries top man of equipment safety standards, Paul Skyrme , sees this post and will come on and give us his expert view?


Has any forum member asked for a Declaration of Conformity from EV charging equipment manufacturers and received one?
Parents
  • Hi Graham, I don't own a copy of bs1363-2 and was unaware of clause 7.1(b). However my point was that the quoted reg is unclear. If it meant that the socket outlet should have bs1363/EV printed on its rear by the OEM, then that is what it should say. not "a socket outlet complying with bs1363-2 marked "EV" on its rear"

    The same reg says an additional label shall be provided on the "front face" which is what I was referring to at the start of the above post. It does say "except where there is no possibility of confusion" and I apologise if my post caused any.
Reply
  • Hi Graham, I don't own a copy of bs1363-2 and was unaware of clause 7.1(b). However my point was that the quoted reg is unclear. If it meant that the socket outlet should have bs1363/EV printed on its rear by the OEM, then that is what it should say. not "a socket outlet complying with bs1363-2 marked "EV" on its rear"

    The same reg says an additional label shall be provided on the "front face" which is what I was referring to at the start of the above post. It does say "except where there is no possibility of confusion" and I apologise if my post caused any.