This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

EV CHARGING EQUIPMENT

I am hearing from my network of contractors, that have actually read the new 722, that they have been asking charging equipment manufactures for documentary proof to comply with Note 5 of 722.411.4.


They are getting knocked back for asking or in one case a Declaration that says the particular device complies with BS 7671. I think that is wrong to declare that as BS 7671 is an installation safety standard and not a product standard. I believe that as a minimum the equipment must comply with the Low Voltage Directive and be CE marked. I also believe that manufacturers have to issue a Declaration of Conformity. 


BS 7671 722 has numerous references to the various standards required such as BS EN 61851 that the equipment must comply with. I am thinking it may be illegal to offer the sale of equipment that does not comply with the Low Voltage Directive and is not CE marked?


I am hoping the countries top man of equipment safety standards, Paul Skyrme , sees this post and will come on and give us his expert view?


Has any forum member asked for a Declaration of Conformity from EV charging equipment manufacturers and received one?
Parents

  • OlympusMons:




    Chris Pearson:






    ...

    But we are getting away from JP's OP. ..




     



    Apologies John. 

     


     




    Ah! But! I am trying to steer it back around.


    Does anyone have one of those Masterplug 13-amp EV charging stations to hand or fixed to the front wall of their house or somewhere similar? If so please go and dismantle it and post a picture of where the socket is marked EV on its rear.


    If if I see one of these whilst undertaking the preparation of an EICR I will definitely be taking it apart to have a look inside it.


    Andy Betteridge 

Reply

  • OlympusMons:




    Chris Pearson:






    ...

    But we are getting away from JP's OP. ..




     



    Apologies John. 

     


     




    Ah! But! I am trying to steer it back around.


    Does anyone have one of those Masterplug 13-amp EV charging stations to hand or fixed to the front wall of their house or somewhere similar? If so please go and dismantle it and post a picture of where the socket is marked EV on its rear.


    If if I see one of these whilst undertaking the preparation of an EICR I will definitely be taking it apart to have a look inside it.


    Andy Betteridge 

Children
No Data