Sparkingchip:
So if you have a nice shiny new M’plug EV charging station attached to the wall of the house just make sure that the electrician that installed it also installed a 30 mA double pole type A RCD in the consumer unit or circuit upstream of it, because apparently that single pole type AC RCBO is not fit for purpose.
Helpful guidance from the manufacturer?
Being single pole it doesn’t even count as an emergency switch and there’s no discrimination with the RCD that is required upfront of it, it fails to pass inspection on any points at all.
It’s going to take twenty five minutes to write the observations up on an EICR.
Andy Betteridge
Sparkingchip:
So if you have a nice shiny new M’plug EV charging station attached to the wall of the house just make sure that the electrician that installed it also installed a 30 mA double pole type A RCD in the consumer unit or circuit upstream of it, because apparently that single pole type AC RCBO is not fit for purpose.
Helpful guidance from the manufacturer?
Being single pole it doesn’t even count as an emergency switch and there’s no discrimination with the RCD that is required upfront of it, it fails to pass inspection on any points at all.
It’s going to take twenty five minutes to write the observations up on an EICR.
Andy Betteridge