EV CHARGING EQUIPMENT

I am hearing from my network of contractors, that have actually read the new 722, that they have been asking charging equipment manufactures for documentary proof to comply with Note 5 of 722.411.4.


They are getting knocked back for asking or in one case a Declaration that says the particular device complies with BS 7671. I think that is wrong to declare that as BS 7671 is an installation safety standard and not a product standard. I believe that as a minimum the equipment must comply with the Low Voltage Directive and be CE marked. I also believe that manufacturers have to issue a Declaration of Conformity. 


BS 7671 722 has numerous references to the various standards required such as BS EN 61851 that the equipment must comply with. I am thinking it may be illegal to offer the sale of equipment that does not comply with the Low Voltage Directive and is not CE marked?


I am hoping the countries top man of equipment safety standards, Paul Skyrme , sees this post and will come on and give us his expert view?


Has any forum member asked for a Declaration of Conformity from EV charging equipment manufacturers and received one?
Parents

  • ebee:

    Well we could all use isolating transformer and configure the ouput as our own TNS just for the charger




    Unless I've missed something, I don't think this is any improvement on using TT earthing system just for the charger ... except more expensive?


    As I see it, the situation would still be that you need separation below ground between conductive parts connected to the TN-S  earthing system, and those connected to the PME earthing system (otherwise you don't comply with 722.411.4.1), and avoid simultaneous contact above ground otherwise you don't comply with 411.3.1.1 ?

Reply

  • ebee:

    Well we could all use isolating transformer and configure the ouput as our own TNS just for the charger




    Unless I've missed something, I don't think this is any improvement on using TT earthing system just for the charger ... except more expensive?


    As I see it, the situation would still be that you need separation below ground between conductive parts connected to the TN-S  earthing system, and those connected to the PME earthing system (otherwise you don't comply with 722.411.4.1), and avoid simultaneous contact above ground otherwise you don't comply with 411.3.1.1 ?