This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

EV CHARGING EQUIPMENT

I am hearing from my network of contractors, that have actually read the new 722, that they have been asking charging equipment manufactures for documentary proof to comply with Note 5 of 722.411.4.


They are getting knocked back for asking or in one case a Declaration that says the particular device complies with BS 7671. I think that is wrong to declare that as BS 7671 is an installation safety standard and not a product standard. I believe that as a minimum the equipment must comply with the Low Voltage Directive and be CE marked. I also believe that manufacturers have to issue a Declaration of Conformity. 


BS 7671 722 has numerous references to the various standards required such as BS EN 61851 that the equipment must comply with. I am thinking it may be illegal to offer the sale of equipment that does not comply with the Low Voltage Directive and is not CE marked?


I am hoping the countries top man of equipment safety standards, Paul Skyrme , sees this post and will come on and give us his expert view?


Has any forum member asked for a Declaration of Conformity from EV charging equipment manufacturers and received one?
Parents

  • Sparkingchip:




    Sparkingchip:

    Isn’t supposed to mention BS EN 61851?


    Andy Betteridge 




     

    Or is it a consumer unit to connect a charger to rather than a charger itself?


    Andy Betteridge 

     




    It sits in between the consumer unit and the charger, as it disconnects the circuit protective conductor downstream of it in the cable using SWA between this unit and the charger needs to be considered very carefully.


    Andy Betteridge

Reply

  • Sparkingchip:




    Sparkingchip:

    Isn’t supposed to mention BS EN 61851?


    Andy Betteridge 




     

    Or is it a consumer unit to connect a charger to rather than a charger itself?


    Andy Betteridge 

     




    It sits in between the consumer unit and the charger, as it disconnects the circuit protective conductor downstream of it in the cable using SWA between this unit and the charger needs to be considered very carefully.


    Andy Betteridge

Children