OK you say what if a N-E fault occurs on the cable or elsewhere in car or charger. This will trip any RCD as a large current (compared to 30mA) will be diverted to the earth conductor, bypassing the N side of the RCD. The small DC signal (lets say 12 mA or whatever) will not prevent this trip. I
In any case to be dangerous we need a second fault, say a lost N elsewhere and a person effectively connected to ground touching exposed conductive parts of the car.
The danger will be a bit more if the car has finished charging but is still connected, but under this condition we still need a fault and a person well connected to ground, whatever the RCD does.
Under the same conditions I can see that a large number of consumers will be exposed to exactly the same danger in many other situations.
It seems to me that this is getting out of proportion as it is not possible to avoid any risk without making cars class 2 which seems to be unacceptable to "the powers that be". The supposed solution is not available to be risk free, RCD or not. Because the car body cannot be isolated from the supply system (even if the supply is TT, and that is a severe problem in urban environments) we have some level of risk from faults. Such faults are very unusual (when did you last find an appliance with a N-E fault in the connecting cable?) and it is probably folk law that RCD tripping in the presence of a high fault current is prevented by 12mA of DC, although the 30mA value may be somewhat increased. It seems to me that the RCD reliability is probably less good than the cable fault scenario, and so we are not making any difference with increased complexity.
gkenyon:
BS 7671 does have another solution in Annex 722 for separation of the vehicle from the installation, if pockets are deep enough.
Chris Pearson:
gkenyon:
BS 7671 does have another solution in Annex 722 for separation of the vehicle from the installation, if pockets are deep enough.And still this thread rumbles on.
Graham if you had a PME supply (could be single or three phase) and deep pockets (deep enough to have bought an EV in the first place) which method would you choose please?
Please also clear up what may seem to be an elementary question. I understand the need to separate the earthing arrangements of different systems, which could lead to difficulty placing either a TT earthing rod or a reference electrode. So does the separation have to be from a PME electrode (in my case, I assume that would be a street lamp by the corner of my property) to an installation electrode; or does it have to be from a service cable to an installation electrode?
davezawadi:
I am not disagreeing with you Graham, just trying to air the subject as fully as possible.
The next question may be slightly painful to some, and that is: Who in a suitable position to understand the problem signed up to accepting standards which are basically faulty in concept? There appears to be no suitable way in an urban environment where an electric vehicle can be guaranteed to be free of the PME system, even if the supply is "TTed" with a local electrode. So quite simply the now common problem of a lost N connection can make a car significantly dangerous however many RCDs of whatever type are in place. The answer is that we now need to monitor electrode to neutral voltage and disconnect the vehicle completely, including the Earth and control wires, should this voltage exceed some value, say 55V RMS for discussions sake. This disconnection needs to be permanent needing a reset back to the no fault condition and substantially instant. Such a device is fairly simple and cheap to manufacture, but we don't have a requirement to fit one. Instead we have all kinds of very expensive RCDs which do not provide anything like the same level of protection. So lets make a new standard, to incorporate such a device in every charge point, which fixes the problem for good.
The separation has to be between the separate TT installation earth electrode, and any buried uninsulated metalwork connected to the PME earthing system.
AJJewsbury:
In the spirit of debate still, why does a TT system (or voltage monitoring electrode for a 'unicorn' device) have to be separate from the influence of a PME system? Someone touching the car isn't going to be standing on some theoretically perfect 0V plane, they're going to be stood on the same ground the car is standing on (or at least within a 1m or so of it). So if there are a few tens of volts from a PME system (or from any other source) under the car, surely it's better for the EVSE c.p.c. to be at that same voltage or at least as close as we can make - so we're minimising the voltage difference between the car and the ground it's stood on - rather than some perfect 0V which is only represetantive of the ground potential half a mile away. Isn't that the principle of equipotentiality?
So bang in a rod as close as you can to the (centre of?) the parking space (not hitting buried services notwithstanding) and be done.
Measurement earth electrode
- If the TT electrode is too close (say within 1 m), it's effectively touching PME, so you've not got separation and therefore no point in the electrode. You also need to allow for ground subsidance.
- You might well then want to argue about the person not standing at the "general mass of earth", but sometimes the voltage drops off quite quickly, even a couple of metres, and there's no guarantee the potential at the feet of a person will be that at the TT earth electrode.
- Conversely, and because of the previous point, in small curtilage properties, you might well be standing over some metalwork (say incoming gas or water pipe) connected to the PME earth, and in certain cases, you simply return the PME touch voltage ... this of course means that going to the trouble of TT in many dwellings is pointless !