This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Metal - clad buildings and the confused forum member.

One of the members has queried ESQCR bonding/earthing PME requirements for the above. So its worth spending a little time putting across the companies requirements. Where metal-clad buildings incorporate a steel-frame that utilises steel vertical beams that are within the foundations, the steel frame will provide a good connection with the earth which will effectively limit the earth potential rise.

A PME service may be provided to a metal-clad building provided the following criteria are satisfied:


1. The metal cladding is bonded to the steel-frame.

2. The supply is either three-phase with less than 40% unbalance or the supply is single - phase and the frame to earth impedance is les than 20ohms.

Regards, UKPN?

Parents
  • Former Community Member
    0 Former Community Member
    A PME service may be provided to a metal-clad building provided the following criteria are satisfied:


    1. The metal cladding is bonded to the steel-frame.

    2. The supply is either three-phase with less than 40% unbalance or the supply is single - phase and the frame to earth impedance is les than 20ohms.


    3? The building has only ONE service connected, if more than one service is required due to the building being split into individual units (terrace like), those subsequent services can only be TT?


    True or false?


    Regards


    BOD
Reply
  • Former Community Member
    0 Former Community Member
    A PME service may be provided to a metal-clad building provided the following criteria are satisfied:


    1. The metal cladding is bonded to the steel-frame.

    2. The supply is either three-phase with less than 40% unbalance or the supply is single - phase and the frame to earth impedance is les than 20ohms.


    3? The building has only ONE service connected, if more than one service is required due to the building being split into individual units (terrace like), those subsequent services can only be TT?


    True or false?


    Regards


    BOD
Children
No Data