Metal - clad buildings and the confused forum member.

One of the members has queried ESQCR bonding/earthing PME requirements for the above. So its worth spending a little time putting across the companies requirements. Where metal-clad buildings incorporate a steel-frame that utilises steel vertical beams that are within the foundations, the steel frame will provide a good connection with the earth which will effectively limit the earth potential rise.

A PME service may be provided to a metal-clad building provided the following criteria are satisfied:


1. The metal cladding is bonded to the steel-frame.

2. The supply is either three-phase with less than 40% unbalance or the supply is single - phase and the frame to earth impedance is les than 20ohms.

Regards, UKPN?

Parents



  • I stand looking at installations and end up up with so many questions in my head.

    e4bffd996ab1139305dc0f900a75c938-original-20200517_133131.jpg
Reply



  • I stand looking at installations and end up up with so many questions in my head.

    e4bffd996ab1139305dc0f900a75c938-original-20200517_133131.jpg
Children
No Data