Alan Capon:gkenyon:
That's very interesting ... how is the TT installation immediately adjacent to the PME supplied installation separated from the PME earthing system?For us, the issue would be two or more PME services into different areas of a steel building. It would be possible for the steelwork of the building to carry diverted neutral currents, for which it almost certainly would not be rated.
Regards,
Alan.
That I understand.
However, connecting extraneous-conductive-parts to the MET (or inadequate separation of the TT earthing system) effectively connects the installation to PME, This may cause a problem for either diverted Neutral currents in the LV system as before (the TT earth electrode resistance may be very small, and if not properly separated ... it's pretty much connected?). Also, the issue I pointed out previously.
Alan Capon:gkenyon:
That's very interesting ... how is the TT installation immediately adjacent to the PME supplied installation separated from the PME earthing system?For us, the issue would be two or more PME services into different areas of a steel building. It would be possible for the steelwork of the building to carry diverted neutral currents, for which it almost certainly would not be rated.
Regards,
Alan.
That I understand.
However, connecting extraneous-conductive-parts to the MET (or inadequate separation of the TT earthing system) effectively connects the installation to PME, This may cause a problem for either diverted Neutral currents in the LV system as before (the TT earth electrode resistance may be very small, and if not properly separated ... it's pretty much connected?). Also, the issue I pointed out previously.
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.
Continue to the IET registration site