Metal - clad buildings and the confused forum member.

One of the members has queried ESQCR bonding/earthing PME requirements for the above. So its worth spending a little time putting across the companies requirements. Where metal-clad buildings incorporate a steel-frame that utilises steel vertical beams that are within the foundations, the steel frame will provide a good connection with the earth which will effectively limit the earth potential rise.

A PME service may be provided to a metal-clad building provided the following criteria are satisfied:


1. The metal cladding is bonded to the steel-frame.

2. The supply is either three-phase with less than 40% unbalance or the supply is single - phase and the frame to earth impedance is les than 20ohms.

Regards, UKPN?

Parents
  • A bit of light reading:


    7. EARTHING

    7.1 Separate Services Originating outside the Building

    7.1.1 Where services are to be installed in accordance with subsection 5.2 in low-rise domestic and commercial (retail or offices) premises of conventional construction (brick, stone, concrete), interconnection of the neutral cores of the separate services, either within the building or through the fabric of the building, is unlikely. PME connections, via CNE service cables, shall normally be used.

    7.1.2 In steel-framed or steel-clad buildings (eg industrial units), interconnection of the neutral cores of separate service cables, through the fabric of the building, shall be avoided. Where it is not practicable to establish a single Intake Position, with an incoming PME connection and internal SNE sub-services provided by the Landlord, BNO or Customers, the service connections to the separate units shall be SNE. These may be derived directly from the LV Network or via a feeder pillar, with an incoming CNE connection.

    7.1.3 Where Premises in a steel-framed or metal-clad building with an existing CNE connection are to be divided into separate Premises and where it is not practicable to establish a single Intake Position, the existing service shall be disconnected and removed and each of the newly divided Premises connected externally, using SNE cables. Any other existing CNE connections in the same building, not affected by the division of Premises, may remain as they are, unless problems caused by the diversion of neutral currents are reported.

    https://www.enwl.co.uk/globalassets/get-connected/cic/icpsidnos/g81-library/1---design--planning/5-design--planning/es287---connections-to-multi-occupancy-buildings.pdf


    That is the recommendation, however implementation may vary.


    Andy Betteridge
Reply
  • A bit of light reading:


    7. EARTHING

    7.1 Separate Services Originating outside the Building

    7.1.1 Where services are to be installed in accordance with subsection 5.2 in low-rise domestic and commercial (retail or offices) premises of conventional construction (brick, stone, concrete), interconnection of the neutral cores of the separate services, either within the building or through the fabric of the building, is unlikely. PME connections, via CNE service cables, shall normally be used.

    7.1.2 In steel-framed or steel-clad buildings (eg industrial units), interconnection of the neutral cores of separate service cables, through the fabric of the building, shall be avoided. Where it is not practicable to establish a single Intake Position, with an incoming PME connection and internal SNE sub-services provided by the Landlord, BNO or Customers, the service connections to the separate units shall be SNE. These may be derived directly from the LV Network or via a feeder pillar, with an incoming CNE connection.

    7.1.3 Where Premises in a steel-framed or metal-clad building with an existing CNE connection are to be divided into separate Premises and where it is not practicable to establish a single Intake Position, the existing service shall be disconnected and removed and each of the newly divided Premises connected externally, using SNE cables. Any other existing CNE connections in the same building, not affected by the division of Premises, may remain as they are, unless problems caused by the diversion of neutral currents are reported.

    https://www.enwl.co.uk/globalassets/get-connected/cic/icpsidnos/g81-library/1---design--planning/5-design--planning/es287---connections-to-multi-occupancy-buildings.pdf


    That is the recommendation, however implementation may vary.


    Andy Betteridge