Ipf Measurement on a 3-phase system

Hello All,
While checking an EIC and comparing design values vs measured values, a few fundamental questions have been puzzling me and I would be grateful of any advice or comments.
The installation is an embedded LV generator connected to the site 11kV ring via a 1.5MVA transformer. It’s a TN-S system with the N-E link at the transformer. The cables from the generator to the breaker panel are L=3x300, N=2x300, PE=1x240. The breaker panel is considered the point of connection and where Ipf and Ze were measured; Ipf=8.58kA and Ze=0.02Ohms.
  1. The calculated 3-phase symmetrical fault at the breaker panel (not including the generator contribution) was ~34kA (assuming a 250MVA fault level at 11kV) i.e. significantly higher that the measured Ipf. This lead me think that the actual fault level at 11kV must be much lower than 250MVA. On reflection, I’m thinking that the Ipf measurement is however a worst case measurement, as the meter only measures the impedance on the LV side of the transformer and the downstream cables i.e. assumes an ‘infinite source’ on the 11kV side, so the measured Ipf should be much higher than 8.58kA?

  • Maybe the Ipf needs to be multiplied by 2, as the measurement was with a 1-phase meter? The On-Site Guide states that ‘For three-phase supplies, the maximum possible fault level will be approximately twice the single-phase to neutral value.’ Thinking about this multiply by 2 (a round-up of 1.732), while this may be an acceptable approximation for domestic installations, I don’t think it is for an installation like this. Simply doubling the measured L-N value assumes that L and N impedances are the same (they are not) and doesn’t allow for the additional transformer winding impedance for a phase-phase fault. My understanding is also that a 3-phase (symmetrical) fault is effectively a single-phase calculation, so doubt the accuracy of this x2 factor in this case.

  • Could the discrepancies be due to meter inaccuracies at these low impedance readings e.g. a Ze measurement of 0.01Ohms vs 0.02Ohms has a significant impact on Ipf. Should the contractor be using a more specialist meter?

Thanks.

Parents
  • Thinking about this multiply by 2 (a round-up of 1.732)

    My understanding is that 2x is meant to be an exact doubling - not a round up of √3. As you say, the assumption is that L & N conductors have the same impedance - with a bolted 3-phase fault, the fault itself effectively forms an artificial N point - so as with any balanced load, the N currents cancel and so the impedance of the N conductor makes no contribution to the loop impedance. So looking at any one individual phase, compared with the single phase fault case (which the loop meter measured when connected L-N) we have the same driving voltage but half the conductor length, so all else being equal we'd have double the current. (For a fault between just two of the three lines, where the N currents wouldn't entirely cancel, we might indeed have a √3 factor to consider).


    If you know the relative impedances of your L and N conductors you should, in principle at least, be able to adjust the 2x factor to better suit your situation. Although in practice, as others have already mentioned, loop meters are unlikely to give you an accurate starting figure so close to such a large supply, so might not be worth the effort.


     
    as the meter only measures the impedance on the LV side of the transformer and the downstream cables i.e. assumes an ‘infinite source’ on the 11kV side

      As I understand it most loop meters work on the principle of drawing a known current and noting the corresponding drop in voltage to calculate the impedance - as such they do take into account the entire supply, including the HV side (within the meter's limitations at least). A milli-Ohm on the HV side does make considerably less difference than a milli-Ohm on the LV side and will be scaled down accordingly by the transformer's ratio within your reading. (BS 7671's description of Earth fault loop impedance isn't exactly helpful in that regard).


       - Andy.
Reply
  • Thinking about this multiply by 2 (a round-up of 1.732)

    My understanding is that 2x is meant to be an exact doubling - not a round up of √3. As you say, the assumption is that L & N conductors have the same impedance - with a bolted 3-phase fault, the fault itself effectively forms an artificial N point - so as with any balanced load, the N currents cancel and so the impedance of the N conductor makes no contribution to the loop impedance. So looking at any one individual phase, compared with the single phase fault case (which the loop meter measured when connected L-N) we have the same driving voltage but half the conductor length, so all else being equal we'd have double the current. (For a fault between just two of the three lines, where the N currents wouldn't entirely cancel, we might indeed have a √3 factor to consider).


    If you know the relative impedances of your L and N conductors you should, in principle at least, be able to adjust the 2x factor to better suit your situation. Although in practice, as others have already mentioned, loop meters are unlikely to give you an accurate starting figure so close to such a large supply, so might not be worth the effort.


     
    as the meter only measures the impedance on the LV side of the transformer and the downstream cables i.e. assumes an ‘infinite source’ on the 11kV side

      As I understand it most loop meters work on the principle of drawing a known current and noting the corresponding drop in voltage to calculate the impedance - as such they do take into account the entire supply, including the HV side (within the meter's limitations at least). A milli-Ohm on the HV side does make considerably less difference than a milli-Ohm on the LV side and will be scaled down accordingly by the transformer's ratio within your reading. (BS 7671's description of Earth fault loop impedance isn't exactly helpful in that regard).


       - Andy.