This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Cable table which column to use

Hi


Im currently doing a bit of circuit design and am a bit rusty. I’m planning to use a 3 core swa for a single phase circuit. Do I choose the 2core cable single phase column in The regs book current capacity tables even though im using a three core cable or the three or four core cable column? Some of the tables show a little asterix denoting ‘with or without a protective conductor’ which would help in my instance, however table 4d4a doesn’t show this. 

Thanks in advance

Peter
Parents
  • HI Baldyhugh


    If you look at the columns on table 4D4A  - Reference method C for example - column 2 is for single phase AC (It says this at the top of the column) and the next column 3 says that it is for three phase. 


    Hope this helps ;-)


    Kind Regards

    Tatty
Reply
  • HI Baldyhugh


    If you look at the columns on table 4D4A  - Reference method C for example - column 2 is for single phase AC (It says this at the top of the column) and the next column 3 says that it is for three phase. 


    Hope this helps ;-)


    Kind Regards

    Tatty
Children
No Data