It trips when the test button is pressed, but I can't fire it off with my Megger MFT1741.
When these were being installed they were being tested by applying voltage without recording a trip time, rather than applying current and recording the trip time.
So is expecting to test it as I would a modern RCD appropriate?
I have advised that replacement is required, being a 500 mA device in a domestic property, utter regardless of if I can get it to trip with a Megger MFT or not, but stand to be corrected if need be.