It looks like a RCD, it feels like a RCD and it smells like a RCD. Crabtree BS4293.

844e2f6350ee349f550bbd9e10cebe00-huge-20200728_110736.jpg
Parents
  • Missing from the simplified diagram for the tester is the fuse or breaker in series with the 50v winding, so that if you do have a TN system by dint of bonded plumbing or similar, there is something to protect the transformer from total destruction (or perhaps a high wattage resistor and a warning lamp).

    But that is not a VO ELCB - that really  is an early RCD, or CO ELCB as first known - the give-away is the absence of the pair of earth connections, one for the installation CPC and one  for the terra-firma  electrodes - shown as F and E in the lower diagram.

    Still it is indeed time to change it, perhaps  for a 100mA time delay or a 30mA one, depending on the RCD arrangements for the rest of the set-up.
Reply
  • Missing from the simplified diagram for the tester is the fuse or breaker in series with the 50v winding, so that if you do have a TN system by dint of bonded plumbing or similar, there is something to protect the transformer from total destruction (or perhaps a high wattage resistor and a warning lamp).

    But that is not a VO ELCB - that really  is an early RCD, or CO ELCB as first known - the give-away is the absence of the pair of earth connections, one for the installation CPC and one  for the terra-firma  electrodes - shown as F and E in the lower diagram.

    Still it is indeed time to change it, perhaps  for a 100mA time delay or a 30mA one, depending on the RCD arrangements for the rest of the set-up.