AJJewsbury:Chris Pearson:Sparkingchip:
If it’s domestic, Building Regulations limits the number of lights per switch to six.Which regulation?
And what about a chandelier with say, 8 lamps or more?The advise "A single switch should normally operate no more than six light fittings with a maximum total load of 100 circuit-watts" is from the Domestic Building Services Compliance Guide - referred to by AD L1A (and possibly others, I haven't checked), I guess the underlying actual building regulation would be L1:
L1. Reasonable provision shall be made for the conservation of fuel and power in buildings by:
:
(b) providing fixed building services which–
:
(ii) have effective controls;
:
"Effective controls" means that they switch on and off reliably.
The six to a switch rule is supplementary information in guidance only, so very far from a regulation.
AJJewsbury:Chris Pearson:Sparkingchip:
If it’s domestic, Building Regulations limits the number of lights per switch to six.Which regulation?
And what about a chandelier with say, 8 lamps or more?The advise "A single switch should normally operate no more than six light fittings with a maximum total load of 100 circuit-watts" is from the Domestic Building Services Compliance Guide - referred to by AD L1A (and possibly others, I haven't checked), I guess the underlying actual building regulation would be L1:
L1. Reasonable provision shall be made for the conservation of fuel and power in buildings by:
:
(b) providing fixed building services which–
:
(ii) have effective controls;
:
"Effective controls" means that they switch on and off reliably.
The six to a switch rule is supplementary information in guidance only, so very far from a regulation.
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.
Continue to the IET registration site