Crimping of flexible cord conductors

Like most of us, I often crimp flne strand conductors, especially for screw terminals but do not do this for domestic lamp holders and roses etc.

I thought that I would check Section 526 (Electrical Connections) of the Regs but did't find a clear statement of requirements for crimped ends. 

I was particularly unsure of what 526.9.1 was specifying for fine wire conductors "conductor ends shall be suitably treated".


Any guidance or comment would be appreciated.


Regards
Parents
  • Former Community Member
    0 Former Community Member
    dressing neutrals in RCBO boards. Shorten the existing tail


    When I've posted previously and questioned the use by some manufacturers of either 2 mm2 or 2,5 mm2 neutral tails on a 32 or 40 A RCBO in a board containing 70 deg C equipment and outgoing circuits, the topic bombed............


    Regards


    BAD
Reply
  • Former Community Member
    0 Former Community Member
    dressing neutrals in RCBO boards. Shorten the existing tail


    When I've posted previously and questioned the use by some manufacturers of either 2 mm2 or 2,5 mm2 neutral tails on a 32 or 40 A RCBO in a board containing 70 deg C equipment and outgoing circuits, the topic bombed............


    Regards


    BAD