IR fault causing live tests to fail in strange way
Hi all
Had a strange thing happen yesterday.
RCD on split DB tripping on a ring circuit fault. Tested all three conductors to each other at 0.02 meg.
Separated circuit and found redundant part of leg going though kitchen had fault. Kitchen had new ring and redundant part was put in strip connectors and plastered in wall. Disconnected kitchen part and made ring into 2 16A radials. (DB had spare 16A MCBs).
Anyway, the strange part.
Before splitting circuit I tested Zs on 3 wire low setting. Tripped. This was not expected as at 0.02 meg the leakage should only be approx 0.01mA.
The other circuits only had approx 2mA leakage current which was found out when I ramp tested the RCD at the DB with all circuits off, then with all circuits but the faulty one on. All off tripped at 23mA. All on (except faulty one) 21mA leaving 2 mA leakage on circuits. Low current Zs at 15mA plus leakage from other circuits = 17.01mA. Shouldn't have tripped, but did.
Second:
This is the really confusing one. On testing the RCD from a socket on the faulty circuit it would not trip, even at 500mA.
However, when testing at the DB with the faulty circuit's MCB off it tripped fine on x1 on both sides of the cycle.
After rectifying the fault the Zs and RCD tests done from the sockets were okay.
Strange behavior on live tests from an IR fault.
I cannot work out why:
1/  An insulation resistance fault with not enough earth leakage would cause the RCD to trip on a low current Zs test.
2/ An insulation resistance fault would prevent an RCD from tripping even when using 500mA. (Even with part of the test current flowing back though neutral through the fault 500mA should have still tripped it).
Any thoughts about this?
  • Ah ok thanks. Yes I did get it the wrong way round got it sorted now I get what you meant cheers
  • Update:
    I've just been round to check that he has sorted out the earthing issue. He has. He's not an electrician, he's a plumber but is capable of doing that.
    He wasn't able to find what was causing the fault and that's why he called me.
    However, I made a mistake when I said that the earthing was also a problem at that socket as when I rechecked the socket in question that I had tested the RCD from originally it is not one of those that had the bad earth, is was one in another room.
    That still leaves the question as to why the IR fault caused an RCD test with 500mA to stop the RCD from tripping when tested at that socket.
    Still a mystery.