Unusual MCB

Here's an interesting one.

Federal Electric 20A MCB. Had no type on it and was taking a long time to trip. Opened one up and discovered why it didn't have a type.

Others with it were ECC but virtually the same design. Only thermal. Both are plug in types called stab-lok and are bakerlite.


No instantaneous trip mechanism. Only a thermal one.



34200b5e07a12e120f5fc679b8b1b9aa-huge-mcb-with-no-instantanious-trip-mechanism-4.jpg
Parents
  • The RCD part will of course deal with L-E faults, but not a L-N short circuit.


    Let's put the short circuit near to the CU with a loop impedance of 0.2 Ω and so a PSSC of 1150 A - that might heat up the bimetallic strip pretty sharpish. However, at the end of a circuit where the impedance might be 1.0 Ω or more, and if the short circuit has a little more than a negligible impedance, it might cook for long enough to do some damage.


    What did the 15th Edn (or even 14th Edn) require? Surely they must have been compliant!
Reply
  • The RCD part will of course deal with L-E faults, but not a L-N short circuit.


    Let's put the short circuit near to the CU with a loop impedance of 0.2 Ω and so a PSSC of 1150 A - that might heat up the bimetallic strip pretty sharpish. However, at the end of a circuit where the impedance might be 1.0 Ω or more, and if the short circuit has a little more than a negligible impedance, it might cook for long enough to do some damage.


    What did the 15th Edn (or even 14th Edn) require? Surely they must have been compliant!