Preparing a flat for renting

Hi all,

I would be very grateful for some advice. 

My daughter is having her Edinburgh 1st floor flat prepared for renting and it needs some work highlighted by an electrical safety report. Some things have been noted as requiring remedial work that seem odd to me:
  • Two sockets are noted as being wired in Aluminium Twin & Earth cable. Is this likely? It looks to me like stranded copper.  Would it need replacing even if it is as this would be a pig of a job as the wiring is under a laminate floor.

  • The electrician has quoted for adding rubber grommets to all socket back boxes. I know that this is good practice but is it necessary before a property can be rented.?

  • The gas meter is plastic with metal pipes in and out. It is in the ground at the front of the house. Immediately through the wall is the termination point for the DNO supply with a big earth terminal with the rising (copper) gas pipe a few inches away. The Electrician says that the incoming gas supply must be bonded to the Flat main earth point, i.e. up the stairs and across a doorway and not the the building main earth point. Is he correct?


I have a photo but I can't work out how to upload it. It says drag but that doesn't seem to work.
Parents
  • Thanks all.

    The gas meter is in a semi buried box against the front wall of the building and immediately through the wall is the DNO incomer with the copper gas pipe to the flat above very close. The boiler is directly above supplied by a 2.5mmsq 16A supply.

    The CU for the flat is in the middle of the building surrounded by laminate flooring so it would be a pig of a job to get a 10mmsq wire from the CU to the boiler.

    My question is therefore is it acceptable to bond the gas pipe to the DNO earth terminal, which is presumeably connected to the CU earth, or does it have to be direct from the CU? If so, which reg says so.

    I'll try again with the photo of the 2.5mmsq cable254c4b84c2d0b8517f7826954a587354-original-20200730_141505.jpg
Reply
  • Thanks all.

    The gas meter is in a semi buried box against the front wall of the building and immediately through the wall is the DNO incomer with the copper gas pipe to the flat above very close. The boiler is directly above supplied by a 2.5mmsq 16A supply.

    The CU for the flat is in the middle of the building surrounded by laminate flooring so it would be a pig of a job to get a 10mmsq wire from the CU to the boiler.

    My question is therefore is it acceptable to bond the gas pipe to the DNO earth terminal, which is presumeably connected to the CU earth, or does it have to be direct from the CU? If so, which reg says so.

    I'll try again with the photo of the 2.5mmsq cable254c4b84c2d0b8517f7826954a587354-original-20200730_141505.jpg