mapj1:Mike M:
I take it those labels where the phase to phase voltage was 400 were being applied as part of a client request and not a requirement of some BS standard ?well it was in l the IEE wiring regs of the day -which is what it was called long before the the IEE became the IET and BSI got involved in all this electricity stuff.
I am going back to about 1980; but there are quite a few installations from that era.
Yes, the requirement in the 16th Edition BS 7671:1992 and its amendments,was any voltage (U or U0) above 250 V "and where presence not expected", or where in separate enclosures but simultaneously accessible, needed a voltage warning label indicating the voltage.
I'm fairly certain the change was made in 16th Edition BS 7671:2001, to pretty much the current requirement based on U0 of 230 V in any enclosure.
The logic of the current requirement likely circles around two factors:
mapj1:Mike M:
I take it those labels where the phase to phase voltage was 400 were being applied as part of a client request and not a requirement of some BS standard ?well it was in l the IEE wiring regs of the day -which is what it was called long before the the IEE became the IET and BSI got involved in all this electricity stuff.
I am going back to about 1980; but there are quite a few installations from that era.
Yes, the requirement in the 16th Edition BS 7671:1992 and its amendments,was any voltage (U or U0) above 250 V "and where presence not expected", or where in separate enclosures but simultaneously accessible, needed a voltage warning label indicating the voltage.
I'm fairly certain the change was made in 16th Edition BS 7671:2001, to pretty much the current requirement based on U0 of 230 V in any enclosure.
The logic of the current requirement likely circles around two factors: