AFDD performance standards, installation for a timber framed new build

Hi,


I'm building a house based on a SIPS timber frame, and I'm going through the process of designing the wiring.  I'll be installing the electrics myself and have someone to certify the work.


I have been considering the electrical design for the building and looking at AFDD as a means of providing additional protection. Watching some of the testing videos done by John Ward on YouTube I note that different devices from manufacturers seem to behave very inconsistently. 


Given the large investment (~ £150 per device) I'd be interested to hear the forums opinions on the quality standards in force. I was quite happy to invest in these devices at first, but I'm not convinced that the quality between manufacturers is nearly good enough.


Tom
Parents
  • Hi Thomas.


    I think you would be better off putting in a comprehensive fire detection system, sprinklers, or both.  Using "LSZH" type cables rather than PVC insulated will also be a benefit for two reasons, a) less smoke and acidic gas produced during a fire, and b) XLPE insulated conductors will dramatically reduce (in theory to zero) the chance of arcing occurring within damaged cables.


    AFDDs, in my view, are not a panacea that some might have you believe, and they will not detect ohmic heating type faults (which probably account for most electrically started fires).


    I can provide you some research work (yet unpublished) if you PM me with your details.  It might be interesting to you.
Reply
  • Hi Thomas.


    I think you would be better off putting in a comprehensive fire detection system, sprinklers, or both.  Using "LSZH" type cables rather than PVC insulated will also be a benefit for two reasons, a) less smoke and acidic gas produced during a fire, and b) XLPE insulated conductors will dramatically reduce (in theory to zero) the chance of arcing occurring within damaged cables.


    AFDDs, in my view, are not a panacea that some might have you believe, and they will not detect ohmic heating type faults (which probably account for most electrically started fires).


    I can provide you some research work (yet unpublished) if you PM me with your details.  It might be interesting to you.