TT Earthing Systems - Interest by New Zealand

Former Community Member
Former Community Member
I am the chair of a Standards NZ committee charged with the production of a technical report to the NZ regulator regarding the possible use of the TT earthing system in NZ.   Currently, NZ uses the MEN earthing system (as does Australia), being similar to the PME earthing system used in the UK but with an earth electrode being required in each electrical installation to assist in keeping the voltage to earth of the neutral conductor of the LV reticulation close to zero.   Otherwise the MEN system is TN-C-S and relies on the PEN conductor as a return path to clear earth faults by the operation of OCPDs.   The use of RCDs is now required for most sub-circuits to provide additional shock protection.  


As is well known, TN systems are not perfect and a broken or high impedance PEN conductor causes the livening of earthed and bonded surfaces, including the chassis of EVs when they are plugged in to EV charging equipment.   It is noted that the IET Wiring Rules do not permit the use of PME systems to supply EV charging equipment unless the voltage on earthed surfaces is held to a non-lethal value.  
 


Without going into further detail, the committee, in preparing a report, remains concerned about and seeks information on two possible problems.   


The first is how to attain at reasonable cost a TT earthing electrode system that does not exceed 100 ohms to earth in many NZ locations where the soil resistivity and the seasonal variation of this is high.   Does it cost a fortune to do this in the UK?    We have difficulty at many sites in reducing substation earthing mat and rod systems to less than 10 ohms and sometimes that is not achievable.




The second is how to be reasonably sure that the RCDs in any TT installation will be regularly tested every six months or so by the users of the installation?  RCDs are not perfect but are much more important safety devices when used in a TT installation than in a TN installation.   Therefore regular testing appears to be important to maintain safety.    With non-domestic installations this should not be a problem as their regular testing (by pushbutton) can be linked to annual building inspections or included in maintenance schedules.  However, how does the UK ensure - if it does - that the occupants of domestic TT installations regularly check the operation of their RCDs?   One sensible suggestion made by a committee member was that the regular RCD checking could be linked to the six-monthly call by our Fire and Emergency Service to check the batteries in fire alarms installed in houses.   That might prompt a few people to check their RCDs.    


 


Since I was intending to ask about the practicability of 100 ohm earth electrode systems in the UK, I thought that I should also enquire about the regular testing of RCDs in domestic installations.  


I should be grateful for any comments or suggestions.

 

P M R Browne BE(Elect) FIET FENZ

Parents
  • Do NZ domestics often have 3-phase supplies? (It's rare in the UK - hence the lack of appetite for that kind of cut-off device here). Three phase is a bit more common on the European continent for domestic supplies - but far from universal I think, and some places (e.g. France) I believe has been phasing it out in favour of single phase - but France (along with much of southern Europe) much prefers TT anyway.


    TT'ing an entire installation, since we're trying to avoid the influence of a broken MEN, can be tricky since any metallic services (e.g. water or gas pipes) that are continuous to neighbouring properties could import the very MEN voltage you're trying to avoid. TT'ing a small area, such as a detached garage, is sometimes simpler. Another option which I don't think has been mentioned yet, but has often been done in the UK is to TT just the charge point itself - i.e. insulate the installation's PE conductor at the charge point and connect it to a local rod instead - where the charge point contains its own RCD (as most seem to these days) it can be as simple as that. As with any transition to TT it needs a little care to ensure there can't be faults between the incoming live conductors (before the RCD) and TT earthing system, which can be easier if the charge point has an insulating enclosure, or an additional RCD upstream can mitigate that risk.


     
    the MEN system and no doubt the PME system provides safety from line to earth faults by the high fault current that returns back to the transformer via the PEN conductor that then operates the MCB or blows the sub-circuit or service fuse to interrupt the phase supply.

    That does raise the "interesting" problem of mixed disconnection times. I presume you have requirements for disconnection times not unlike ours for TN systems - e.g. max 0.4s for small final circuits, but anything up to 5s for anything else - and potentially longer again for faults on the public supply network. During a L-PE fault the PE/MEN/PEN conductor will be dragged up to something approaching half the line voltage (a pretty hazardous 115-120V say) at the point of the fault until the overcurrent device opens. I doubt that a few extra electrodes of tens or even hundreds of Ohms each will help much (other than to raise the voltage on the soil immediately surrounding each electrode) since the main potential divider (the L and MEN/PE conductors feeding the fault) are likely to be far less than one Ohm. That voltage in then imposed on any metalwork connected to the earthing system - including our EV.  Normally "importing" an earth fault from upstream of the final circuit or outside of the installation it mitigated in two ways - firstly by the interior of most buildings being substantially insulating so there's no widespread true earth potential to complete the shock circuit, and by anything metallic that might introduce an true earth potential (e.g. gas & water supply pipes) being solidly bonded to the installation's earthing system. Outdoors however, on damp ground and random metallic things (like fences & gates) unlikely to be bonded - those mitigations don't apply and so people could be subject to the full fault voltage for the full disconnection time. A TT system has advantages on that score - not only should it be immune to 'importing' earth faults from TN parts of the system, any earth faults with the TT system (even upstream of the circuit feeding the EV charge point) typically disconnect far more quickly than by fuses - even a time delayed RCD should open with 200ms or even 150ms at a decent earth fault current.


      - Andy.
Reply
  • Do NZ domestics often have 3-phase supplies? (It's rare in the UK - hence the lack of appetite for that kind of cut-off device here). Three phase is a bit more common on the European continent for domestic supplies - but far from universal I think, and some places (e.g. France) I believe has been phasing it out in favour of single phase - but France (along with much of southern Europe) much prefers TT anyway.


    TT'ing an entire installation, since we're trying to avoid the influence of a broken MEN, can be tricky since any metallic services (e.g. water or gas pipes) that are continuous to neighbouring properties could import the very MEN voltage you're trying to avoid. TT'ing a small area, such as a detached garage, is sometimes simpler. Another option which I don't think has been mentioned yet, but has often been done in the UK is to TT just the charge point itself - i.e. insulate the installation's PE conductor at the charge point and connect it to a local rod instead - where the charge point contains its own RCD (as most seem to these days) it can be as simple as that. As with any transition to TT it needs a little care to ensure there can't be faults between the incoming live conductors (before the RCD) and TT earthing system, which can be easier if the charge point has an insulating enclosure, or an additional RCD upstream can mitigate that risk.


     
    the MEN system and no doubt the PME system provides safety from line to earth faults by the high fault current that returns back to the transformer via the PEN conductor that then operates the MCB or blows the sub-circuit or service fuse to interrupt the phase supply.

    That does raise the "interesting" problem of mixed disconnection times. I presume you have requirements for disconnection times not unlike ours for TN systems - e.g. max 0.4s for small final circuits, but anything up to 5s for anything else - and potentially longer again for faults on the public supply network. During a L-PE fault the PE/MEN/PEN conductor will be dragged up to something approaching half the line voltage (a pretty hazardous 115-120V say) at the point of the fault until the overcurrent device opens. I doubt that a few extra electrodes of tens or even hundreds of Ohms each will help much (other than to raise the voltage on the soil immediately surrounding each electrode) since the main potential divider (the L and MEN/PE conductors feeding the fault) are likely to be far less than one Ohm. That voltage in then imposed on any metalwork connected to the earthing system - including our EV.  Normally "importing" an earth fault from upstream of the final circuit or outside of the installation it mitigated in two ways - firstly by the interior of most buildings being substantially insulating so there's no widespread true earth potential to complete the shock circuit, and by anything metallic that might introduce an true earth potential (e.g. gas & water supply pipes) being solidly bonded to the installation's earthing system. Outdoors however, on damp ground and random metallic things (like fences & gates) unlikely to be bonded - those mitigations don't apply and so people could be subject to the full fault voltage for the full disconnection time. A TT system has advantages on that score - not only should it be immune to 'importing' earth faults from TN parts of the system, any earth faults with the TT system (even upstream of the circuit feeding the EV charge point) typically disconnect far more quickly than by fuses - even a time delayed RCD should open with 200ms or even 150ms at a decent earth fault current.


      - Andy.