TT Earthing Systems - Interest by New Zealand

Former Community Member
Former Community Member
I am the chair of a Standards NZ committee charged with the production of a technical report to the NZ regulator regarding the possible use of the TT earthing system in NZ.   Currently, NZ uses the MEN earthing system (as does Australia), being similar to the PME earthing system used in the UK but with an earth electrode being required in each electrical installation to assist in keeping the voltage to earth of the neutral conductor of the LV reticulation close to zero.   Otherwise the MEN system is TN-C-S and relies on the PEN conductor as a return path to clear earth faults by the operation of OCPDs.   The use of RCDs is now required for most sub-circuits to provide additional shock protection.  


As is well known, TN systems are not perfect and a broken or high impedance PEN conductor causes the livening of earthed and bonded surfaces, including the chassis of EVs when they are plugged in to EV charging equipment.   It is noted that the IET Wiring Rules do not permit the use of PME systems to supply EV charging equipment unless the voltage on earthed surfaces is held to a non-lethal value.  
 


Without going into further detail, the committee, in preparing a report, remains concerned about and seeks information on two possible problems.   


The first is how to attain at reasonable cost a TT earthing electrode system that does not exceed 100 ohms to earth in many NZ locations where the soil resistivity and the seasonal variation of this is high.   Does it cost a fortune to do this in the UK?    We have difficulty at many sites in reducing substation earthing mat and rod systems to less than 10 ohms and sometimes that is not achievable.




The second is how to be reasonably sure that the RCDs in any TT installation will be regularly tested every six months or so by the users of the installation?  RCDs are not perfect but are much more important safety devices when used in a TT installation than in a TN installation.   Therefore regular testing appears to be important to maintain safety.    With non-domestic installations this should not be a problem as their regular testing (by pushbutton) can be linked to annual building inspections or included in maintenance schedules.  However, how does the UK ensure - if it does - that the occupants of domestic TT installations regularly check the operation of their RCDs?   One sensible suggestion made by a committee member was that the regular RCD checking could be linked to the six-monthly call by our Fire and Emergency Service to check the batteries in fire alarms installed in houses.   That might prompt a few people to check their RCDs.    


 


Since I was intending to ask about the practicability of 100 ohm earth electrode systems in the UK, I thought that I should also enquire about the regular testing of RCDs in domestic installations.  


I should be grateful for any comments or suggestions.

 

P M R Browne BE(Elect) FIET FENZ

  • Sparkingchip:

    If we could easily remove dangerous voltages under fault conditions by simply knocking a metal rod into the ground it would have been done for over a hundred years, but it ain’t that simple.


    The question is, do you want to remove external influences on the earthing system within an electrical installation by relying on RCD protection to limit the effect of faults within the installation?


    Andy Betteridge 


    That's the nice thing about the Neutral Earthing Resistor approach - the PE remains at a safe voltage even during L-PE faults so while you have to depend on RCDs for disconnection, you don't depend on disconnection for shock protection. So the reliability of RCDs becomes somewhat less of an issue.


    Not much use for the OP though I guess as he won't have separate N and PE conductors in the distribution system.


       - Andy.


  • Former Community Member
    0 Former Community Member
    Thank you for the continuing contributions to the above subject, which are grist to the mill for us where the requirement for LV earthing is limited to driving in a spike electrode where bonding to concrete reinforcing is not possible.   


    The warnings concerning the interaction of earthing electrodes in close proximity is also appreciated as if we were to convert part of a MEN installation to TT to supply EV charging and its close environs, there would need to a good separation between the driven earth and the constructed TT earth.    I take it that the reference to a neutral earthing resistor was to an IT system, which I understand is commonly used (not in NZ) to provide a reliable supply to important loads such as hospital theatres or some industrial premises.     


    Lyle, I have heard of bentonite as an earthing enhancing material to use around an earthing electrode but not "chemrod".  I wonder if that might be helpful here.      


    In respect to EV charging, which is a main driver of the possible move to permit the use of the TT system in NZ, I have noted, having been advised of it, that there is an amendment to BS 7671 that permits the use of a device that effectively monitors the integrity of the PEN conductor by measuring its voltage to earth and disconnects the supply in the event of that voltage exceeding 70 V for more than 4 seconds.   If such devices were reliable, the provision of such would likely be a much cheaper solution to converting part of a MEN installation to TT operation.   TT may still be preferable for some installations but it is the fear of a broken PEN conductor while an EV is plugged in to a charger that is a major fear here.   With the great majority of our electricity generation being from renewable energy sources, our government is keen to promote the uptake of EVs but needs EV charging to be a safe operation to the extent that can be provided.    We shall continue to monitor the possibilities.   


    Regards


    Peter Browne
  • I take it that the reference to a neutral earthing resistor was to an IT system

    Similar to IT systems, but not quite the same in some details. Most IT systems either have the live conductors entirely isolated from Earth, or have a deliberate resistance that's usually high enough that any shock current is limited to safe levels; also the consumer's earth electrode can be separate from the source's.


    With the neutral earthing resistor approach, the resistance might be much lower - so as to limit an L-PE fault to perhaps several amps (rather than a few milliamps) - but the source and consumer's earthing systems are solidly connected together (as well as to Earth) - the result being that the earth fault current doesn't raise the voltage on any earthed parts by more than a few volts (instead the voltage on the (insulated) N is raised instead). So there's no hazardous voltages either between different exposed-conductive-parts or between exposed-conductive-parts and Earth (as there can be with both TN and TT systems). I originally found the proposal in an old paper (I think it was one of the Cahier Technique ones) where, if I recall correctly, they described it as modified TN-S or hybrid TN-S/TT system (neither of which properly describe it to my mind). As I said it won't be much use if you're starting with a distribution system that doesn't have separate PE and insulated N conductors (let alone existing installations that rely on low L-PE loop impedances), but if it's of academic interest I can see if I can dig the article up again. I believe it is used in some HV systems for earth fault detection - but as far as I know it's rare for LV.

     
    there is an amendment to BS 7671 that permits the use of a device that effectively monitors the integrity of the PEN conductor by measuring its voltage to earth and disconnects the supply in the event of that voltage exceeding 70 V for more than 4 seconds.

    BS 7671 permits a couple of different designs of such devices - one type references the PE/PEN voltage to a local electrode, the other just monitors L-N voltage and tries to infer a broken PEN from that.


    The first suffers the disadvantage that the local electrode has to be independent of the MEN earthing systems - otherwise it can be fooled if the ground it's planted in has a raised potential due to the broken PEN - so similar issues to creating a local TT system (although the electrode resistance can safely be higher). The second approach as the disadvantage that if the system is fed from a 3-phase distribution system (even if the installation itself is entirely single phase) it's quite possible (if not particularly likely) for the combination of unbalanced loads to pull the severed PEN conductor to a hazardous voltage above true Earth without the L-N voltage being outside a normal range (e.g. 230V+10%-6% for the UK).


    If you have a 3-phase supply and can verify that all three L-L voltages are "normal", an artificial N/Earth point can be deduced from them, which in turn can be used to compare with the voltage on the PE/PEN conductor - which is far more reliable - but obviously of no use for single phase installations (which the vast majority of domestics and small commercials are in the UK).


       - Andy.
  • I was under the impression that the Zappi charger had sorted the concerns re lost neutral on all systems, single-phase and three-phase without the need for electrodes. 7671 didn’t recognise because commercial patents were pending. Perhaps someone more clued in on the EV charging side could confirm or otherwise. 

  • I don't think as a matter of principle BS 7671 would include a patented device for anything.


    The new 772 now has a provision in 722.411.4.1 in indents iii, iv and v for manufactuers to bring novel products to the market products that deliver the required level of safety. As BS 7671 is not a product standard the Note 5. provides guidance on the requirement for devices to meet product standards.
  • Thanks John, I fully understand that from the 7671 perspective but from my reading of the product blurb, if the device is installed as per manufacturers instruction then any concerns with respect to loss of neutral are at least brought to a tolerable risk level. The idea that NZ would dump MEN in favour of TT just to quell the concerns raised about loss of neutral with respect to EV roll out seems superfluous if a simple commercial product is available as an alternative.
  • Peter Browne:

    With the great majority of our electricity generation being from renewable energy sources, our government is keen to promote the uptake of EVs but needs EV charging to be a safe operation to the extent that can be provided.    We shall continue to monitor the possibilities.   


    So am I correct in understanding that the NZ Govt wants to promote EVs, but will not do so until it has decided how to deal with the infrastructure?


    If so, that is rather the opposite of what we have in UK - full steam ahead on EVs including zero vehicle excise duty and subsidies for EVCPs regardless of whether the energy can be supplied. When my local substation's transformer was manufactured in 1959 (the same year as I was ? ) it would probably have served half as many houses and certainly no EVCPs or high-powered electric showers.


  • My house was built in the 1960’s and has a looped service, the cable comes into my garage then loops back out to supply the house next door, as I understand it the house next door will need a new independent supply before either or both houses can have an EV charging point.


    Andy Betteridge
  • Former Community Member
    0 Former Community Member
    Andy, thanks for the explanation of the neutral earthing resistor.  However, the MEN system and no doubt the PME system provides safety from line to earth faults by the high fault current that returns back to the transformer via the PEN conductor that then operates the MCB or blows the sub-circuit or service fuse to interrupt the phase supply.   


    I don't think that we have ever had a TN-S LV system in NZ - if so, it's been lost in the mists of antiquity, even for NZ's comparatively short history.   A few of our EDBs use resonant neutral earthing at zone substations to permit 11 kV feeders to remain in service with a permanent earth fault on one phase - that is a well established distribution practice in some parts of the world.   Expensive to install so it's not widespread.   


    As for the UK, the government here in NZ (pushed by our Greens) is also hell for leather in respect to promoting the adoption of EVs and the phasing out of ICEVs altogether in the next 10 to 20 years..  But I'm sure it remains largely ignorant of the problem of EV charging equipment being supplied from MEN systems.    Our NZ EV charging guidelines documents require the use of supplies from MEN installations as there is no available alternative at present.   Our regulator is well aware - even if the ESI here has not been hammering the need for an alternative because of the risks of broken PEN conductors - mainly in services rather than in the LV reticulation. 


    We would not look for a wholesale change from MEN, just the ability to use TT for, say, a selected distribution board supplied from a MEN main switchboard, if that is a safe solution to the problem (having due regard to the need to have good separation between the MEN earth electrode and the TT earth earth electrode) .   


    So there is bound to be interest in devices that will reliably detect broken PENs and interrupt all live conductors in such an event.   Might be a much cheaper solution!   


    I'm aware that, with a three phase supply, it would be possible to derive the TN-C neutral voltage as a reference against the voltage on the PEN conductor but, as has been said, that won't apply for single or two phase supplies to domestic premises.  Hence I would think that an earth reference electrode would be required, located well away physically from the MEN earth electrode.   


    It has been a good discussion so far.   It will all help as I'm preparing to write a report on TT for my committee to submit to the regulator.   


    Regards


    Peter Browne
  • Former Community Member
    0 Former Community Member
    Hi Peter,


    We have a device that is used for EV Charging in the UK which does not require an earth rod or indeed any reference to Earth to reliably work, the device needs a 3 phase supply but single or 3 phase loads can be protected on the load side. Importantly our technology cannot be set on a fault condition for example a Voltage between N-Vn over 70v as per BS7671 A1


    If you wish for more information then please feel to contact me on matt@matt-e.co.uk


    Kind Regards


    Matt