Site fabricated wooden trunking/capping
Former Community Member
Saw this in a wooden summerhouse, the owner has created his own wooden capping to conceal the cables of a ring final circuit. I was wondering if this might create a safe zone issue where it runs along the bottom edge of the room. The cable is obviously not "buried in a wall at a depth < 50mm but could somebody inadvertently screw something to it. Is it concealed wiring or wooden trunking? Would it get a code if doing a EICR?
Andy, the exact 2 methods I was looking at last night, 12 and 40. Its a good point though to use table 4D2, a T&E is also just a plain ol multicore cable as well as a 'insulated and sheathed flat cable'
Andy, the exact 2 methods I was looking at last night, 12 and 40. Its a good point though to use table 4D2, a T&E is also just a plain ol multicore cable as well as a 'insulated and sheathed flat cable'