whjohnson:
I'll sometimes run a 1.00mm from a B6A rather than a 2.5mm for a FCU, especially when room is tight and the load demands only a 3A fuse at the destination end.
No point in running a bigger cable to provide capacity which most likely will never be used.
Regulation 524.1 (via Table 52.3) requires a minimum 1.5 mm2 for power circuits (i.e. not lighting circuits or auxiliary/control circuits) in sheathed cable. Yes, a reduction for a specific appliance is permitted in Table 52.3, but that's only in flex to the appliance itself, not from the mcb to the appliance.
whjohnson:
I'll sometimes run a 1.00mm from a B6A rather than a 2.5mm for a FCU, especially when room is tight and the load demands only a 3A fuse at the destination end.
No point in running a bigger cable to provide capacity which most likely will never be used.
Regulation 524.1 (via Table 52.3) requires a minimum 1.5 mm2 for power circuits (i.e. not lighting circuits or auxiliary/control circuits) in sheathed cable. Yes, a reduction for a specific appliance is permitted in Table 52.3, but that's only in flex to the appliance itself, not from the mcb to the appliance.