MCB size for dedicated fused spurs

A little thought, when installing a new circuit for a fused spur to supply an alarm or something similar, just about everyone uses a standard 2.5mm radial circuit, but the MCB size seems to vary from 16a down to 6. 


part of me (the larger part) thinks, just keep it standard 16a, and another part says to size the breaker to the load 


(I'm a specifier, not installer)
Parents
  • OlympusMons:

    Hi Graham, it could be argued that "an alarm or something similar" would be classed as a "signalling and control circuit", and the minimum CSA of 0.5mm2, or even possibly 0.1mm2 since most alarms are electronic.

    Andy has commented about table 52.3 in this old thread https://www2.theiet.org/forums/forum/messageview.cfm?catid=205&threadid=54291&STARTPAGE=1&FTVAR_FORUMVIEWTMP=Linear

     




    A supply to an alarm system or control system is definitely a power circuit. The function of the circuit is definitely not not "signalling and control".


    The switched live to a timed fan, or the link wire in mains smoke alarms, may well be a control or auxiliary circuit, as would the secondary (alarm circuits themselves) of the fire or intruder alarm.


    If you install the connection unit on a lighting circuit, then I can see an interpretation that the circuit is mainly for lighting, so 1.0 sq mm is OK ... but if it's a dedicated circuit for something else, I think that argument peters off somewhere.


    However, linking back to the original post, I remembered this recent thread: https://communities.theiet.org/discussions/viewtopic/1037/26230


    Which got me thinking that FCUs to BS 1363-4 are not necessarily suitable for termination, without special preparation, 1.0 sq mm (or 1.5 sq mm for that matter) - the manufacturer may choose to state otherwise, of course.


Reply
  • OlympusMons:

    Hi Graham, it could be argued that "an alarm or something similar" would be classed as a "signalling and control circuit", and the minimum CSA of 0.5mm2, or even possibly 0.1mm2 since most alarms are electronic.

    Andy has commented about table 52.3 in this old thread https://www2.theiet.org/forums/forum/messageview.cfm?catid=205&threadid=54291&STARTPAGE=1&FTVAR_FORUMVIEWTMP=Linear

     




    A supply to an alarm system or control system is definitely a power circuit. The function of the circuit is definitely not not "signalling and control".


    The switched live to a timed fan, or the link wire in mains smoke alarms, may well be a control or auxiliary circuit, as would the secondary (alarm circuits themselves) of the fire or intruder alarm.


    If you install the connection unit on a lighting circuit, then I can see an interpretation that the circuit is mainly for lighting, so 1.0 sq mm is OK ... but if it's a dedicated circuit for something else, I think that argument peters off somewhere.


    However, linking back to the original post, I remembered this recent thread: https://communities.theiet.org/discussions/viewtopic/1037/26230


    Which got me thinking that FCUs to BS 1363-4 are not necessarily suitable for termination, without special preparation, 1.0 sq mm (or 1.5 sq mm for that matter) - the manufacturer may choose to state otherwise, of course.