MCB size for dedicated fused spurs

A little thought, when installing a new circuit for a fused spur to supply an alarm or something similar, just about everyone uses a standard 2.5mm radial circuit, but the MCB size seems to vary from 16a down to 6. 


part of me (the larger part) thinks, just keep it standard 16a, and another part says to size the breaker to the load 


(I'm a specifier, not installer)
Parents
  • The circuit that provides power for the smoke alarms or alarm panel must be a power circuit, as it provides power to that equipment.

    Hence my point about any signalling or control circuit drawing some power in order to operate - where do we draw the line? If everything that draws power is a power circuit then there seems little room left for signalling or control circuits. Is the supply to a relay coil power or a signal? - or to an indicator lamp? or to a TTL input? All require a current flow.


    In many ways it shouldn't matter - if power and lighting circuit are operating with similar protective devices in similar environments it doesn't really make sense for the c.s.a. requirements to be different.


    I can perhaps see that there's perhaps an issue with energy let-though with MCBs which the UK has traditionally glossed over = but a 1.5mm min c.s.a. regardless of type of protective device or circuit arrangement isn't really a proper solution to that either. Likewise if it's a physical robustness concern 1.5mm² might be reasonable for pulling singles into conduit like the French do, but there doesn't seem to be a good reason for specifying anything higher than 1.0mm² for the sheathed cables that are normal UK practice.


       - Andy.
Reply
  • The circuit that provides power for the smoke alarms or alarm panel must be a power circuit, as it provides power to that equipment.

    Hence my point about any signalling or control circuit drawing some power in order to operate - where do we draw the line? If everything that draws power is a power circuit then there seems little room left for signalling or control circuits. Is the supply to a relay coil power or a signal? - or to an indicator lamp? or to a TTL input? All require a current flow.


    In many ways it shouldn't matter - if power and lighting circuit are operating with similar protective devices in similar environments it doesn't really make sense for the c.s.a. requirements to be different.


    I can perhaps see that there's perhaps an issue with energy let-though with MCBs which the UK has traditionally glossed over = but a 1.5mm min c.s.a. regardless of type of protective device or circuit arrangement isn't really a proper solution to that either. Likewise if it's a physical robustness concern 1.5mm² might be reasonable for pulling singles into conduit like the French do, but there doesn't seem to be a good reason for specifying anything higher than 1.0mm² for the sheathed cables that are normal UK practice.


       - Andy.